Thread: 300.11 B

  1. #1
    Join Date
    Jun 2008
    Location
    Dallas, Tx
    Posts
    569

    300.11 B

    Am I allowed to shoot ceiling wire without it being supported at the other end?

  2. #2
    Join Date
    Mar 2010
    Location
    Lake of the Ozarks
    Posts
    1,032
    Quote Originally Posted by xformer View Post
    Am I allowed to shoot ceiling wire without it being supported at the other end?
    Negative.

    1N73LL1G3NC3 15 7H3 4BILI7Y 70 4D4P7 70 CH4NG3.

  3. #3
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    33,021
    Quote Originally Posted by xformer View Post
    Am I allowed to shoot ceiling wire without it being supported at the other end?

    Do you mean an inaccessible area of the ceiling?
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  4. #4
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,544
    The section you cited, 300.11(B) clearly requires the independent support wire to be secured at the bottom end. 300.11(B)(2) permits you to connect the bottom end to the ceiling grid. There are clips designed for this purpose that let you secure the bottom end without bowing the grid. These clips can also serve as the required identification of the independent support wire.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)