    An existing 100 amp load is supplied by a 3-phase 100 amp breaker. A new 100 amp load is being installed. The system can't handle the load of both the existing and the new at the same time, and there will never be a need to run them both at the same time. What do you think about using a Manual Transfer Switch to select which load will get power and be allowed to operate?
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  2. #2
    Join Date
    Aug 2004
    Northern illinois
    Posts
    16,538
    Quote Originally Posted by charlie b View Post
    sounds workable to me
    Bob
  3. #3
    Join Date
    Jul 2006
    Posts
    7,640
    Not at all an unusual application for it. Done all the time.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  4. #4
    Join Date
    Jul 2005
    Tennessee
    Posts
    15,899
    Keep in mind if there if any type controller such as a motor starter/contactor is involved you might accomplish the same thing by use of a selector switch in the control circuits.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.
  5. #5
    Join Date
    Feb 2003
    Illinois
    Posts
    23,544
    Might be able to be accomplished with a breaker interlock device. Those are sometimes used for residential generator interlock purposes.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
  6. #6
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,976
    We have done this several times as well. Works just like 3-pole, 3-way switch.
    Rob
    All responses based on the 2014 NEC unless otherwise noted
  7. #7
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,939
    I haven't visited the site yet. I may be able to do that next week. There is a question of whether the panel has room for an additional 100 amp breaker. So the thought is to intercept the existing branch circuit from the panel's 100 amp breaker (serving an electric unit heater), insert the MTS, and run the other side of the MTS to the new 100 amp load (a heat pump). Sounds like it is a viable option. Thanks for the comments.
  8. #8
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,976
    Funny that you've mentioned a unit heater, we recently had a room that stored the building window washing unit that they wanted to heat during the winter. Since getting a new circuit there was nearly impossible we intercepted the washer circuit and installed a 100 amp MTS. During the winter months when the window washer isn't used the building engineer switches from washer to unit heater.
    Rob