    Hi all,
    I received this picture from a colleague asking if the installation is allowed. The plug feeds a UPS. I told him I'll dig more, but it will be nicer to install an outlet and plug the ups there.
    My question is: is there a violation?
    if yes, where does the code address it.
    thanks,
    qasim
  2. #2
    Join Date
    Mar 2013
    Rutland, VT, USA
    Posts
    370
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I would say it violates both a NEC article and the similar OSHA regulation.
    NEC Art. 110.3(B) which states that listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
    OSHA 1910.303(b)(2) states that listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling.
    I doubt that breaker is labeled or listed for use as a receptacle.
  3. #3
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,394
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by i.engrqasim View Post
    Hi all,
    thanks,
    qasim
    How are they getting the EGC to the UPS?
    300.3(B)
    110.3(B)
    Bob
  4. #4
    Join Date
    Aug 2017
    Los Angeles CA
    Posts
    215
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Look at the color coding and the type of plug! (American) NEC has nothing to say about it!
    But still a hack job IMO, and yes Grounding?
  5. #5
    Join Date
    May 2018
    Saudi Arabia
    Posts
    11
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by petersonra View Post
    300.3(B)
    110.3(B)
    there is a grounding bus below. they are getting it from there a separate grounding cable.
  6. #6
    Join Date
    May 2018
    Saudi Arabia
    Posts
    11
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Andy Delle View Post
    our specifications are based on IEC.
    NEC is used for unofficial references.
  7. #7
    Join Date
    May 2018
    Saudi Arabia
    Posts
    11
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by wbdvt View Post
    Thanks.
    especially for the OSHA reference.
  8. #8
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,394
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    might be legal under IEC. not so much with the NEC.