    On half of a switchleg is dimming after a few hours??

    This is a pretty big service area. There are around 80 lights,
    4 trunklines with 2 switchlegs and one emergency circuit.
    Each switchleg has its own roomcontroller.

    So half one switchleg (which is one whole trunkline ) dims after being on for about 5 hours.if u turn off the switch and let the lights rest for a while they will turn bright again for a while This problem only started last week and the buildiny has been up and running wit tennants for 4 months already.
    Just an FYI these lights do not have the dimming wires attached . They are capped off and no;38,^ used.. any ideas?

    Sent from my SM-N950U using Tapatalk

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,978
    Sounds like a loose connection somewhere that is affected by the heat from the load
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  3. #3
    Join Date
    Oct 2017
    Location
    Manteca,Ca
    Posts
    7
    Quote Originally Posted by Dennis Alwon View Post
    Sounds like a loose connection somewhere that is affected by the heat from the load
    I was thinking the same thing. Good good thing its all of the lights. That means its near the beginning of the run

    Sent from my SM-N950U using Tapatalk

  4. #4
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,978
    Could be the switch itself
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  5. #5
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    5,236
    Quote Originally Posted by Dennis Alwon View Post
    Could be the switch itself
    That was my first thought. I've seen a few cases were residential grade switches were used in commercial, 1200 Watts worth lighting put on a 600-watt dimmer, 20a of lighting on a 20a breaker, etc.

    If the switch is the culprit, it will probably be half melted already.
    Electricians do it until it Hertz!

  6. #6
    Join Date
    Feb 2007
    Location
    USA
    Posts
    5,544
    No Dimming hooked up?
    How did you get that past Title 24 lighting controls?