is there any easier explanation.
For example how many #2 Wires I can splice in 8x8x6 splice box?

The limitation is based on the box being big enough to comply with the 6X and 8X rules. If you could get 40-#2's in the box and still comply with the straight and angle pull rules then you would be code compliant.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
still don't get that.
I know to #6. but larger then that.
witch table in code book tells me how much space conductor takes.
i tried to find it but i can't see it.

Again there is no cu in size for larger than #6 conductors and there is not table.
 