    Please help with the model of this GE feeder breaker

    Hello All,
    I'm trying to buy a GE 60A 2 pole breaker that fits this existing residential 240/120V 100A single phase 3 wire panel (some circuit rearrangement will be made to make room for the 60A feeder breaker, and I already did the load calculations for the main panel).
    Thanks a lot.
    Click image for larger version. 

Name:	PC030039.jpg 
Views:	204 
Size:	148.2 KB 
ID:	20358

    Would this residential Q line breaker work?
    https://www.homedepot.com/p/GE-Q-Lin...2160/100676698

    Amazon has this thin one but only 50A (it seems to me in the FAQ says they don't have/make the 60A thin version).
    https://www.amazon.com/General-Elect..._&dpSrc=detail
    Last edited by fandi; 05-17-18 at 12:03 AM.

  2. #2
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,252
    I think your picture is showing a Zinsco panel and breakers, not General Electric. Could be wrong though.
    I live for today, I'm just a day behind.

  3. #3
    Join Date
    Oct 2014
    Location
    Los Angeles
    Posts
    128
    Click image for larger version. 

Name:	P3190082.JPG 
Views:	59 
Size:	59.1 KB 
ID:	20360It's GE per the enclosure
    Also where could I buy the 20A tandem breaker?
    Attached Images Attached Images  

  4. #4
    Join Date
    Feb 2003
    Location
    San Jose, CA
    Posts
    1,515
    Don't know why the cover would be GE but that is definitely a Zinsco panel. GE breakers will not fit. You need Zinsco breakers.
    Curt Swartz
    Electrical Contractor

  5. #5
    Join Date
    Feb 2007
    Location
    USA
    Posts
    5,757
    Ge/Sylvania as well as Challenger used those breakers. I think that is a piggy back unit.


    Oh it also looks like there is no main breaker and thus too many handles.

  6. #6
    Join Date
    May 2003
    Posts
    1,304
    Quote Originally Posted by Sierrasparky View Post
    Ge/Sylvania as well as Challenger used those breakers. I think that is a piggy back unit.


    Oh it also looks like there is no main breaker and thus too many handles.
    It was GTE Sylvania, not GE, but that is a very early Zinsco panel that is well past it's prime.

    GTE bought Zinsco Electrical Products in 1973, & rebranded them as Sylvania.

  7. #7
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,252
    Quote Originally Posted by norcal View Post
    It was GTE Sylvania, not GE, but that is a very early Zinsco panel that is well past it's prime.

    GTE bought Zinsco Electrical Products in 1973, & rebranded them as Sylvania.
    correct, but have no idea why the cover on OP's panel has raised lettering that says "General Electric" - look hard at the picture it is there.
    I live for today, I'm just a day behind.

  8. #8
    Join Date
    May 2003
    Posts
    1,304
    Quote Originally Posted by kwired View Post
    correct, but have no idea why the cover on OP's panel has raised lettering that says "General Electric" - look hard at the picture it is there.
    After looking at it again, someone needed a new cover for the Zinsco, so they beat a GE cover flat. Handyhack strikes again.

  9. #9
    Join Date
    Feb 2003
    Location
    Minnesota
    Posts
    6,926
    Quote Originally Posted by norcal View Post
    After looking at it again, someone needed a new cover for the Zinsco, so they beat a GE cover flat. Handyhack strikes again.
    Yes. That is exactly what the photos show. Zinsco breakers on a Zinsco bus. The "General Electric" on the cover can't change the fact of the guts.
    Another Al in Minnesota

  10. #10
    Join Date
    Jul 2006
    Location
    San Francisco Bay Area, CA, USA
    Posts
    8,108
    Quote Originally Posted by norcal View Post
    After looking at it again, someone needed a new cover for the Zinsco, so they beat a GE cover flat. Handyhack strikes again.
    Nice catch. Yep, you can see where the corners of the cover used to be.