    On a corner grounded three phase delta service the grounded conductor is marked white at the meter base and in the panel. once a three phase branch circuit leaves the panel must you mark the grounded conductor in the branch circuit white ?

  2. #2
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    9,950
    Quote Originally Posted by domnic View Post
    On a corner grounded three phase delta service the grounded conductor is marked white at the meter base and in the panel. once a three phase branch circuit leaves the panel must you mark the grounded conductor in the branch circuit white ?
    Of course. Why wouldn't you?

  3. #3
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,901
    Quote Originally Posted by domnic View Post
    On a corner grounded three phase delta service the grounded conductor is marked white at the meter base and in the panel. once a three phase branch circuit leaves the panel must you mark the grounded conductor in the branch circuit white ?
    it is still the grounded conductor.
    Bob

  4. #4
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,733
    While the code requires that grounded conductor to be identified just like any other grounded conductor, in the 20-30 grounded phase systems that I have seen, I have never seen the grounded conductor so identified.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)