    Quote Originally Posted by romex jockey View Post
    Exactly the jist of the article's reference to GPR

    >>>>



    That nanosecond of GPR is far less damaging if the entire residence assumes 1,000,000 volts

    VS. 1,000,000 volts on one end, 500,000 volts on the other, which is FAR more damaging.

    One can even read this theory into past code cycles. Remember when we didn't bond gas lines? The gas guys would have conniptions....then it evolved to 'within 6' , along with a flashover rationale. , these days we either bond the gas lines or fail inspections.


    ~RJ~
    Yup- electronics are no different than people in a pool or hot tub. Basically the people/electronics are the high resistance and bonding is the ultra low resistance. The goal is to have most of the voltage drop across the bonding due to that ultra low resistance.


    In regards to gas lines- RJ- do you personally have any experience with csst? I know that was a major game changer.


    http://www.npihome.com/tag/american-gas-association/
    I'm in over my head...

  2. #22
    Join Date
    Mar 2003
    Location
    Vermont
    Posts
    1,746
    In regards to gas lines- RJ- do you personally have any experience with csst? I know that was a major game changer.

    No more than any garden variety spark MBrooke , these days we're told to find some part of it that's solid & bond it






    ...ouch!


    ~RJ~

  3. #23
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,639
    Quote Originally Posted by mbrooke View Post
    Yup- electronics are no different than people in a pool or hot tub. Basically the people/electronics are the high resistance and bonding is the ultra low resistance. The goal is to have most of the voltage drop across the bonding due to that ultra low resistance.
    ...
    ...
    More properly, the goal is to have most of the fault current flowing through the bonding, so that the identical voltage drop across person and bonding is low enough not to cause harm to the person.

  4. #24
    Join Date
    Jan 2011
    Location
    United States
    Posts
    7,960
    Quote Originally Posted by GoldDigger View Post
    More properly, the goal is to have most of the fault current flowing through the bonding, so that the identical voltage drop across person and bonding is low enough not to cause harm to the person.
    Oopps, voltage drop as in pulling down the voltage between two points... horrible choice of words.
    I'm in over my head...