User Tag List
Page 1 of 3 123 LastLast
Results 1 to 10 of 24
Thread: Ground Potential Rise
  1. #1
    Join Date
    Jan 2011
    United States
    Posts
    8,326
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    I came across this article which talks about ground potential rise from having unbonded grounding electrodes. Its very eye opening and I wish Mike Holt would do a new letter or a you Tube video on CATV bonding. I know there are many misconceptions about this. At my own home for example the CATV has its own ground rod...
    http://electrical-engineering-portal...e-in-your-home
    what do others think about this article? Right from an electrical theory standpoint?
    I'm in over my head...
  2. #2
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,876
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I have the attention span of a gnat so wading through all that text for about three minutes was about all I could stand.
    If I understood correctly the point of the article is that driving extra ground rods is a bad idea, and you are making things worse if you add extra ground rods that don't tie back to the main service. If that is correct then I agree.
    If you don't think too good, don't think too much.
  3. #3
    Join Date
    Jan 2011
    United States
    Posts
    8,326
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by ActionDave View Post
    Yes- nice synopsis
  4. #4
    Join Date
    Jun 2003
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    10,412
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mbrooke View Post
    Yes- nice synopsis
    Isn’t this the reason for an Inter Systems Bonding Terminal? The one we are required to put in, but no one uses.
    Tom
    TBLO
  5. #5
    Join Date
    Jan 2011
    United States
    Posts
    8,326
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by ptonsparky View Post
    Yes- but you have seen the reality.
  6. #6
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,107
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Theory is mostly accurate.
    NEC does require bonding CATV to electrical system, as well as other systems. Had this requirement even before the intersystem bonding terminal was added.
    You can drive all the rods you want for other systems if that makes you feel good - but they also all need to be bonded together.
    Even when all such systems are bonded, the more direct the lightning strike is the more likely you have temporary rise in voltage in some instances or even certain portions of a premises.
    I live for today, I'm just a day behind.
  7. #7
    Join Date
    Jan 2011
    United States
    Posts
    8,326
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by kwired View Post
    I'd imagine- I remember mike saying that the frequency pulse of lightning is so high that even a few feet of #6 will exhibit significant impedance.
    Xl=2piFL
  8. #8
    Join Date
    Sep 2007
    MP89.5, Mason City Subdivision
    Posts
    222
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    ...At my own home for example the CATV has its own ground rod...
    Around here, they don't even bother with that, let alone connect to the ISBT.
    One of my radio station clients added cable internet in between my usual visits. The CATV tech mounted his first splitter 3 feet from the main ground bar. He left it float, and by the time I discovered it, a surge roared in and took out the cable modem, router and one of the ethernet switches. What a mess.
    Gregg
    I'm just here for the pictures!
  9. #9
    Join Date
    Jan 2011
    United States
    Posts
    8,326
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    Quote Originally Posted by grich View Post
    Bonding is more important than grounding. In fact article 250 is mostly around bonding, not grounding. Grounding has little if anything to do with people and property protection at 600 volts and under.
  10. #10
    Join Date
    Feb 2013
    India
    Posts
    2,546
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    1)Grounding dissipates surge energy lest it should do harm.
    2)In case of Mv to LV accidental contact, grounding on LV side limits ground potential rise.
Posting Permissions
  • You may not post replies
  • You may not edit your posts
