Thread: 250.104 Bonding copper water pipes in house with non metallic supply.

  1. #1
    Join Date
    Feb 2007
    Location
    Alexandria, VA
    Posts
    428
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    250.104 Bonding copper water pipes in house with non metallic supply.

    The plastic water piping system in a house has been completely replaced with copper. The supply to the house is non metallic. 250.104 specifies the location of the point of attached for the bonding jumper on the service/GES end but not on the water pipe. Does this mean I can attached the jumper at any convenient point in the water piping system? I see no requirement for the "first five feet."

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,366
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Yes, you can connect at any point that's accessible.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,006
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    You are correct.. Anywhere is good
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  4. #4
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Replacing plastic with copper? That's a rare bird. Although not required, I run a bonding jumper across both hot and cold water sides, I do not like relying on the idea of the water heater or the tub mixing valve body to do that for me.
    Electricians do it until it Hertz!

  5. #5
    Join Date
    Feb 2007
    Location
    Alexandria, VA
    Posts
    428
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Copper supply line without bonding

    I am the original poster and actually went to this job the other day. The entire 1980s town house, built using plastic water piping, had been re piped with copper. I was surprised to find a copper supply line entering from the basement floor and no GEC back to the panel on the other side of the basement. There were, however, two ground rods. There was the original county inspection sticker on the panel.

    Was there ever a time when this would have been accepted? Copper water supply, plastic piping. ground rods and no water bond?

  6. #6
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    34,006
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    The water pipe connection, where there is 10' or more of metallic piping in the earth, has been around as long as I can remember
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  7. #7
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,837
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Greg1707 View Post
    I am the original poster and actually went to this job the other day. The entire 1980s town house, built using plastic water piping, had been re piped with copper. I was surprised to find a copper supply line entering from the basement floor and no GEC back to the panel on the other side of the basement. There were, however, two ground rods. There was the original county inspection sticker on the panel.

    Was there ever a time when this would have been accepted? Copper water supply, plastic piping. ground rods and no water bond?
    Back then there was no rule to bond it within 5 feet of entry - that came in about 1993 or 1996 NEC IIRC.

    So if it was originally bonded - it probably hit the most convenient place on the piping. When it was changed to non metallic piping that connection was likely removed. Now if there were major work going on when that change was made including electrical work - maybe a chance it would have had GEC run to (or near) the point where it was still metal piping that emerged into the building.
    I live for today, I'm just a day behind.