Thread: Grounded Conductor required?

  1. #91
    Join Date
    May 2018
    Location
    USA
    Posts
    1
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Re:

    Thanks for the question! As a general rule, white and gray are restricted to grounded conductors.

  2. #92
    Join Date
    May 2018
    Location
    Jamaica and london
    Posts
    1,304
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    It could be a metallic raceway. Also how does that impact the need to bring in the grounded conductor?
    Perhaps this is why the UK code has onelook at placing a ground within the metallic raceway in some instances, and requires bonding of all conduits and raceways at both ends with the circuit ground so that if any ground fails, the rest of the grounding circuit still carries the ground and trips the breaker? Or am I reading the textbooks wrong?
    Since a student, even with ARRL Advanced background, know I may be wrong but hoping I understand what I am reading.

  3. #93
    Join Date
    Apr 2016
    Location
    Georgia
    Posts
    526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Adamjamma View Post
    Perhaps this is why the UK code has onelook at placing a ground within the metallic raceway in some instances, and requires bonding of all conduits and raceways at both ends with the circuit ground so that if any ground fails, the rest of the grounding circuit still carries the ground and trips the breaker? Or am I reading the textbooks wrong?
    Since a student, even with ARRL Advanced background, know I may be wrong but hoping I understand what I am reading.
    Are you referring to BS 7671? As I recall this is a derivative of IEC 60364? What you've just described is closer to the equipment grounding conductor, 'EGC' than grounded conductor in NEC. The British counterpart would be a TNS system, if I remember correctly.

  4. #94
    Join Date
    Dec 2018
    Location
    Perrysburg township, OH, USA
    Posts
    1
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)

    Single phase residential transformer

    I just recently read that the H2 connection of a residential distribution transformers primary winding is fed by one hot wire (on H1) and the other end of the primary winding (H2) is connected to the transformers case ground. If that’s correct then what do they use for a neutral ?

  5. #95
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    40,183
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by StvRamnd48! View Post
    I just recently read that the H2 connection of a residential distribution transformers primary winding is fed by one hot wire (on H1) and the other end of the primary winding (H2) is connected to the transformers case ground. If that’s correct then what do they use for a neutral ?
    On a multi grounded neutral system this normal. Neutral/ground are the same thing on such a system.
    I live for today, I'm just a day behind.