Thread: cable in conduit cable end seals

  1. #11
    Join Date
    May 2018
    Location
    Internet
    Posts
    176
    Quote Originally Posted by Dale001289 View Post
    Wrong.


    Sent from my iPhone using Tapatalk
    code reference please

  2. #12
    Join Date
    May 2018
    Location
    Internet
    Posts
    176
    Quote Originally Posted by Dale001289 View Post
    Wrong.
    [QUOTE=Dale001289;1919231]


    501.15(D)(2) exception

    ....by an approved means.....


    article 100

    Approved- acceptable to the authority having jurisdiction

  3. #13
    Join Date
    Apr 2016
    Location
    Georgia
    Posts
    509
    Quote Originally Posted by Wire-Smith View Post
    501.15(D)(2) exception

    ....by an approved means.....


    article 100

    Approved- acceptable to the authority having jurisdiction
    “Approved“ and “Approved Means” are not the same thing -


    Sent from my iPhone using Tapatalk

  4. #14
    Join Date
    May 2018
    Location
    Internet
    Posts
    176
    Quote Originally Posted by Dale001289 View Post
    Wrong.
    are you thinking of listed? its different

  5. #15
    Join Date
    May 2018
    Location
    Internet
    Posts
    176
    Quote Originally Posted by Dale001289 View Post
    “Approved“ and “Approved Means” are not the same thing -


    Sent from my iPhone using Tapatalk
    110.2 Approval. "the conductors and equipment required or permitted by this code shall be acceptable only if approved.

    informational note. see... definitions of approved....."


    once again, code reference please. i don't subscribe to dales electrical code just NEC


    means
    mēnz/
    noun
    [COLOR=#878787 !important][/COLOR]

    • 1.
      an action or system by which a result is brought about; a method.

    put the two together and what do you have?

  6. #16
    Join Date
    Apr 2016
    Location
    Georgia
    Posts
    509
    Quote Originally Posted by Wire-Smith View Post
    are you thinking of listed? its different
    The sealant must be explosion proof vs nonexplosion proof or simply “minimizing gases “ such as duct seal - it must be listed or labeled. Once it has been listed by an approved means it can then be approved the AHJ


    Sent from my iPhone using Tapatalk

  7. #17
    Join Date
    May 2018
    Location
    Internet
    Posts
    176
    Quote Originally Posted by Dale001289 View Post
    The sealant must be explosion proof vs nonexplosion proof or simply “minimizing gases “ such as duct seal - it must be listed or labeled. Once it has been listed by an approved means it can then be approved the AHJ


    Sent from my iPhone using Tapatalk
    code reference please, not everything we use is listed, by what u r saying every electrical installation is in violation right now

  8. #18
    Join Date
    May 2018
    Location
    Internet
    Posts
    176
    Quote Originally Posted by Dale001289 View Post
    The sealant must be explosion proof vs nonexplosion proof or simply “minimizing gases “ such as duct seal - it must be listed or labeled. Once it has been listed by an approved means it can then be approved the AHJ


    Sent from my iPhone using Tapatalk

    TSC is listed for explosion-proof seals

    and no seal completely seals out gases, all of them only minimize


    why the h*** do you think the code allows this?

  9. #19
    Join Date
    Apr 2016
    Location
    Georgia
    Posts
    509
    Quote Originally Posted by Wire-Smith View Post
    TSC is explosionproof
    Exactly TSC is used with cable seals - why don’t you try reading from the beginning post pretty please


    Sent from my iPhone using Tapatalk
    Last edited by roger; 05-31-18 at 06:32 PM.

  10. #20
    Join Date
    May 2018
    Location
    Internet
    Posts
    176
    Quote Originally Posted by Dale001289 View Post
    Exactly TSC is used with cable seals - why don’t you try reading from the beginning post pretty please


    Sent from my iPhone using Tapatalk
    why don't you try reading the code book?


    i agree tsc is for cable seals, always thought that. this post provides no good argument or information
    Last edited by roger; 05-31-18 at 06:32 PM.