    what do you all use for end sealing cables, crouse hinds epoxy TSC? it isn't clearly labelled for this. what else is available?
    i'm talking about when you run cable capable of transmitting gases in rigid, don't open the jacket in the seal off but seal the cable end in the enclosure where it terminates.
  2. #2
    Join Date
    Apr 2004
    Mission Viejo, CA
    Posts
    5,608
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Are we talking about multiconductor cable in conduit?
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2017 NEC unless otherwise noted.
  3. #3
    Join Date
    Apr 2016
    Georgia
    Posts
    526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Wire-Smith View Post
    If you were running ONLY multiconductor cable such as TC-ER or MC-HL (no conduit) you could use the TSC Epoxy Sealing compound along with a TMCX connector. But since the cable is routed within conduit, I believe you'll to have to use a conduit seal - such as EYS - open the jacket/separate the conductors and apply Chico compound.
  4. #4
    Join Date
    May 2018
    Ohio
    Posts
    381
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by rbalex View Post
    yes
  5. #5
    Join Date
    May 2018
    Ohio
    Posts
    381
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dale001289 View Post
    i disagree 501.15(D)(2) exception
    cable w/ gas/vapor-tight sheath
  6. #6
    Join Date
    Apr 2016
    Georgia
    Posts
    526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The cable sheath is not the cable core - That’s why you need the EYS/Chico etc
  7. #7
    Join Date
    May 2018
    Ohio
    Posts
    381
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    did u read the exception, you don't have to open the sheath in a seal-off, just seal cable end at termination
  8. #8
    Join Date
    Apr 2016
    Georgia
    Posts
    526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    There is no approved UL sealant for multiconductor cable ends when installed in conduit - you need a tmcx for that
  9. #9
    Join Date
    May 2018
    Ohio
    Posts
    381
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    doesnt need to be ul approved, just approved (by ahj)
  10. #10
    Join Date
    Apr 2016
    Georgia
    Posts
    526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Wrong.