    The tenant to occupy 5th and 8th floors. How to estimate sharing of HVAC, lights , elevator, fire protection charges, standby generator usage in the absence of submeter? Thanks.
  2. #2
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,285
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Sahib View Post
    Percentage of total square footage? How are other tenants contributing?
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  3. #3
    Join Date
    Feb 2013
    India
    Posts
    2,552
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes, percentage of square footage. Maximum demand also that way? Thanks.
  4. #4
    Join Date
    Jan 2008
    Posts
    9,642
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    As long as usage profiles are the same then square foot percentage. An 8-5 law office use will be very different from a 24-hour data center so a load count and profile would then be better.
    BB+/BB=?
  5. #5
    Join Date
    Feb 2013
    India
    Posts
    2,552
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mivey View Post
    So if the tenant maximum demand is not coincident, it is better to have a separate sub-meter. correct?
  6. #6
    Join Date
    Sep 2008
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I would and it would be an objective way of sharing out the total bill. If that would be permitted by the POCO.
    Si hoc legere scis nimium eruditionis habes.
  7. #7
    Join Date
    Jan 2008
    Posts
    9,642
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    If you do not have a decent approximation of the demand coincidence factor then a separate meter would be needed if you want to assign demand costs with a reasonable degree of fairness.
    BB+/BB=?
  8. #8
    Join Date
    Feb 2013
    India
    Posts
    2,552
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks.
  9. #9
    Join Date
    Feb 2013
    India
    Posts
    2,552
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If the sub-meter as suggested above is not provided but Maximum demand is shared on square foot basis, who will get undue advantage, owner or tenant ?
  10. #10
    Join Date
    Jan 2008
    Posts
    9,642
    Mentioned
    0 Post(s)
    Tagged
    1 Thread(s)
    The one with the highest demand per square foot.