Thread: GEC extended / shared raceway

  1. #1
    Join Date
    May 2018
    Location
    Morris, IL, USA
    Posts
    2

    GEC extended / shared raceway

    We installed an ATS on a 200 amp residential service. The GEC in the main panel was extended using a compression splice, then run through the 2" conduit with the feeders from the ATS and landed at the neutral bus in the ATS where it is bonded. The inspector said that we could not extend the GEC and run through the panel, rather it had to be in a separate raceway directly to the ATS. He cited 250.24. We can find nothing in that article and I mentioned 312.8, but he wouldn't accept it. Thanks in advance for the help, this is my first post.

  2. #2
    Join Date
    May 2018
    Location
    Internet
    Posts
    178
    it has to be as short as possible, i don't have my code book with me so i can't confirm my statement with code reference right now, i would think it should come straight out of ats and down to grounding electrode system

  3. #3
    Join Date
    May 2018
    Location
    Internet
    Posts
    178
    lightning likes short and usually vertical paths

  4. #4
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,937
    Quote Originally Posted by Wire-Smith View Post
    lightning likes short and usually vertical paths
    While true fact is that it probably doesn't make all that much difference
    Bob

  5. #5
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    15,973
    It sounds as if both your neutral and the extended GEC are terminated in the old panel thus tied together thru thru the old panel neutral buss. Is that correct ?
    Assuming the ATS is service rated, you need to seperate the neutrals and equipment grounds in the old panel 250.24(A)(5)
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  6. #6
    Join Date
    May 2018
    Location
    Morris, IL, USA
    Posts
    2
    The neutral and GEC are not bonded at the panel, that connection is now at the ATS.

  7. #7
    Join Date
    May 2011
    Posts
    4,640
    Does the ATS switch the neutral?

  8. #8
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,773
    Quote Originally Posted by bakerelect View Post
    The neutral and GEC are not bonded at the panel, that connection is now at the ATS.
    I don't think you have a code violation. I don't think the code reference he gave you is relevant.
    If you don't think too good, don't think too much.

  9. #9
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,773
    Quote Originally Posted by jaggedben View Post
    Does the ATS switch the neutral?
    Why would that matter?
    If you don't think too good, don't think too much.