    Im in the process of doing a pool for a friend it's in ground with a plastic shell but the top has metal caps for pavers to sit on, when doing the perimeter bond do these caps need to be bonded as well , there are probably about 10-12 peices going around the whole pool there not continous, the caps are pretty much in the dirt , I'm thinking the perimeter grid probably takes care of this but not sure
    Sent from my SM-G950U using Tapatalk
  2. #2
    Join Date
    Apr 2006
    Simi Valley, CA
    Posts
    8,471
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    code says any metal within five feet of the pool.
    I can build anything you want if you draw a picture of it on the back of a big enough check.
    There's no substitute for hard work....but that doesn't mean I'm going to give up trying to find one.
    John Childress
    Electrical Inspector
    IAEI / CEI / C10
    Certified Electrical Inspector
  3. #3
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,153
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    I agree.. A pita job but it needs to be done. I have to do gutters and metal handrails for a sunken in the deck hot tub. Sucks. Why would I want to take stray voltage from the ground and put it on the gutters?
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  4. #4
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,644
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    So the metal caps are not exposed or able to be contacted by a person and are separated by a permanent barrier the paving stones? Wouldn't 680.26(B)(7)Ex#1 cover this?
    Rob
  5. #5
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,167
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dennis Alwon View Post
    A little confused at what you are getting at with this, might just be choice of wording though.
    Intent of equipotential bonding isn't to "ground" the objects in question - it is to bond all objects in the vicinity of the pool user so they are all at same potential - we sort of don't care what potential they are in relation to "ground". The entire pool could be sitting there at 100 volts above ground, but a well installed EPB system will leave the pool users with no clue they are "energized".
    Now that much voltage still likely yields problems at the perimeter of the deck and near other bonded objects, but located away from the pool.
    I live for today, I'm just a day behind.
  6. #6
    Join Date
    Dec 2010
    Tennessee NEC:2017
    Posts
    5,052
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    I've done several concrete pools. They have a metal track that mounts to the top for the liner to hang on. This track is very thin and will be covered with coping stones. The inspectors here make me bond this track. It's a pain because the track is not one continuous piece but several pieces placed end to end. They don't actually touch each other so they are not electrically continuous.
    What I have to do is install a lay-in lug, rated for direct burial, on each section then run a #8 solid conductor around the top of the pool. Then I run a jumper down to the "Halo" #8 that encircles the pool. (equipotential bond wire)
    I argued that the track will be covered with coping and can't be touched and the water is also bonded but made no head-way with the inspectors so I just do it on all pools of that type that I do.
    So to answer the OP's question, yes you need to bond the metal caps.
    If you aim at nothing, you will hit it every time!
  7. #7
    Join Date
    Nov 2016
    Kennewick
    Posts
    143
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Equipotential grid
    You have to bond them unless they meet these exceptions.
  8. #8
    Join Date
    Oct 2015
    US
    Posts
    798
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    Yes there not exposed will be covered by pavers and mortar
  9. #9
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,167
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Little Bill View Post
    I never done a pool, but even though they are not exposed, I would think it is still a good idea to bond them. Kind of no different then having isolated rebar in about same vicinity if it were concrete - seems to have a possibility of being able to introduce a voltage gradient if not bonded to other items and especially between two sections of it that are as you mentioned are all separate pieces.
  10. #10
    Join Date
    Nov 2016
    Kennewick
    Posts
    143
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Mortar is porous so therefore not a permanent barrier