User Tag List
Page 1 of 3 1 2 3 LastLast
Results 1 to 10 of 29
Thread: Wall Oven Whip
  1. #1
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,986
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Wall Oven Whip
    Looking at this wall oven which came from the supplier with a cord and plug connection. I can't recall seeing this type of oven with a cord and plug only hardwired with a factory whip. Looking at the way it's installed (a strap that is large enough for a FMC whip) it's my guess that someone removed the factory whip and installed the cord. Factory whips usually have higher temperature conductors than cord sets and these ovens are not designed for cord an plug. Opinions?
    Click image for larger version.
    Last edited by Little Bill; 06-06-18 at 08:38 AM. Reason: changed "code" to "cord"
    Rob
  2. #2
    Join Date
    Apr 2016
    Georgia
    Posts
    526
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    Looking at this wall oven which came from the supplier with a code and plug connection. I can't recall seeing this type of oven with a cord and plug only hardwired with a factory whip. Looking at the way it's installed (a strap that is large enough for a FMC whip) it's my guess that someone removed the factory whip and installed the cord. Factory whips usually have higher temperature conductors than cord sets and these ovens are not designed for cord an plug. Opinions?
    Vendor data shows fixed connection, no plug.
  3. #3
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,357
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    I have never seen one like that either. They always come with flex not cord....
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  4. #4
    Join Date
    Sep 2008
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dennis Alwon View Post
    Ignorant Brit strikes again....
    What's the difference between a flex and a cord?
  5. #5
    Join Date
    Feb 2003
    New Jersey
    Posts
    3,839
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Besoeker View Post
    Flex is an armored cable (i.e MC or AC cable).
  6. #6
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,357
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by goldstar View Post
    Or FMC (flexible metal conduit)-- flex is a metallic conduit with no conductors in it. Of course, there are conductors in the flex coming from the back of the range but as Trevor stated the wires are usually a higher temperature conductor.
  7. #7
    Join Date
    Feb 2003
    New Jersey
    Posts
    3,839
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    At first glance it looked like a single wall oven which in most cases would require a 30A circuit. However, looking at the KW rating on the nameplate it's 6.4 KW. 6400 divided by 240V = 26 A. 80% of a 30A circuit would be 24A. So, you'll have to go to the next trade size and use a 40A circuit. That being said, I don't know if you'll have the room to mount a 50A receptacle behind the oven. If not, I'd cut the plug off, wire it direct and drop the JB inside the wall.
  8. #8
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    5,332
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    I don't think an oven Is a continuous load.
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  9. #9
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,357
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Agreed
  10. #10
    Join Date
    Sep 2008
    UK
    Posts
    12,703
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thank you both. Always an education here. This for us would be flexible cable or flex.