    I asked a few others here at the company and I now have a hard copy on my desk!
    Reading through the codes I noticed mention of Line Power being incendive. Do you guys know if I need to do anything other than proper bonding on my Line power coming into the power supply and my 24VDC lines going to the alarms?
    I would like to connect everything to the enclosure with plugs and cables ideally.
    Any thoughts or suggestions?

  2. #12
    Join Date
    Apr 2016
    Location
    Georgia
    Posts
    509
    You will need to bond all conduit and cable entering the enclosure. Look at 501.30


    Sent from my iPhone using Tapatalk

  3. #13
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,900
    Quote Originally Posted by Aubrey M View Post
    I asked a few others here at the company and I now have a hard copy on my desk!
    Reading through the codes I noticed mention of Line Power being incendive. Do you guys know if I need to do anything other than proper bonding on my Line power coming into the power supply and my 24VDC lines going to the alarms?
    I would like to connect everything to the enclosure with plugs and cables ideally.
    Any thoughts or suggestions?
    I don't know what you mean by line power being "incendive". Can you cite the code reference that states that?

    Take a close look at 501.140 and see if you qualify to use plug and cord connections.
    Bob

  4. #14
    Join Date
    Jun 2018
    Location
    Sioux Falls, SD USA
    Posts
    5
    I've lookwd back through the book but can't find where I saw it mention about Line Power being incendive. It was probably on a website trying to explain the NEC without actually posting everything.
    Looking over 501.140 and other info this morning it looks like I could get away with a plain old weatherproof enclosure with I used sealed cable glands made for Div2 locations as long as I have the Div2 power supply.
    I think I'm going to play it save and put my Div2 power supply in a Stainless Steel Nema 4X enclosure that will meet Div2 requirements with Div2 cables and plugs. At least that's the plan for now until someone says, "That cost too much" then I may have to rework my BOM a little.
    Thanks for all the help from everyone.