User Tag List
Results 1 to 7 of 7
Thread: Changing three phase voltage
  1. #1
    Join Date
    Aug 2008
    Posts
    408
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    A project I have asked about is 120/240 3phase. I am told by POCO that I could switch to 120/208 3phase.
    A existing piece of equipment I called on I would need to switch heating elements on and a controller so I am thinking against changing voltages.
    What other things should I consider when thinking of changing voltages. And what other pluses and minuses are there.
  2. #2
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    A 120 / 240 3 phase service is a high leg Delta, a 120 / 208 3-phase service is a Wye.
    The latter is generally more versatile, the only real thing you need to look at is equipment that is designed for 230 or 240 volts only... Motors that are not 208- 230 / 460 will not be happy running on 208 volts.
    You need to look at what percentage of loads are single phase and what percent are three phase, cost of the existing service versus a new one, amperage, and so on.
    Heating elements that are designed for 240 volts will put out roughly 75% of their rating at 208 volts.
  3. #3
    Join Date
    Jul 2005
    Tennessee
    Posts
    16,572
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The first step, I would think, is confirm with POCO as to what's available.. some power companies won't even supply 240/120 3 phase any longer,
    Next, list all your equipment and see what requires 240. If 208 is you voltage of choice, It is a fairly simple task to use a comparatively less expensive buck-n-boost transformer on items that are straight 240. If a neutral (120) is involved that option is a bit more complicated or not possible.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.
  4. #4
    Join Date
    Dec 2015
    Texas
    Posts
    195
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by arnettda View Post
    Pluses:
    1) Get to use the 'B' Phase for single phase loads when changing to 3 Phase.
    2) More simple to conduct a short circuit current study (opinion of course)
    3) You don't have to worry about having an atypical voltage that, while small, still represents a potential hazard for connection for maintenance/electricians, etc.
    Minuses:
    1)Resistive loads will increase current to meet same output/or changing of equipment not dual rated 208/240V.
    2)You don't get to say you have a Wild Leg anymore.
    3) Confirm the POCO has 3 Phases readily present and that they won't charge you to extend 3 phase to this location, if not present. A few delta services that I've come across the utility noted the same thing, but would require payment to extend an additional phase at the owner's expense.
  5. #5
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    41,030
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by augie47 View Post
    He said it is high leg system already and that POCO suggested possibly changing to 208/120.
    Quote Originally Posted by tw1156 View Post
    Pluses:
    Minuses:
    Resistance of such loads is usually fixed, so to get same kW output you physically need to replace heating elements. If you leave existing ones they won't be overloaded or overheated, they just put out about 75% of what they did on 240 volts. If marginally sized for the application to begin with then they may not be enough if run on 208.
    I live for today, I'm just a day behind.
  6. #6
    Join Date
    Jul 2006
    Posts
    8,641
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    Yes, or if they are doing something like heating up water, it just takes a little longer if you leave the original heaters in place and give them the lower voltage.
    As I said above, you may not need to change the heating elements if you can just live with it taking longer to get to temperature. I can't see having to change the "controller" though. that's probably coming from someone who wants to sell you more stuff...
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  7. #7
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    10,025
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Minuses:
    If you don't think too good, don't think too much.