    Commerical fryer
    I have commerical fryer restaurant kitchen full load amps of 39 amps. What would be the size of feeder branch circuit breaker be?
    Sent from my SM-G935U using Tapatalk
  2. #2
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,986
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    40 amp branch circuit.
    Rob
  3. #3
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,744
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I would go 50 amps.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  4. #4
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    This is not what I am exactly clear on:
    39x100% = 39 next rating 40 amps
    or
    39x1.25 = 48.75 next rating 50 amps.
    Is commerical fryer continous load or noncontinous load?
  5. #5
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,744
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Almost all heating equipment maintains temperature by cycling power, so non-continuous. I just prefer not loading to 100%, even when it doesn't have to be 125%.
    Larry B. Fine
    Master Electrician
    Richmond, VA
  6. #6
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    40,163
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Longest time a fryer would be drawing full current would be when first turned on until it reaches set point. Most probably reach set point within 10 maybe 15 minutes max - far from three hours needed to call it a continuous load.
    I live for today, I'm just a day behind.
  7. #7
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,986
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    It's not a continuous load so a 40 amp branch circuit would be code compliant. I guess that you could use a 50 amp circuit as well.
    Rob
  8. #8
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I beg to differ that a commercial deep fryer is not a continuous load... Restaurants around here are incredibly busy, and they often have to wait for their fryers to get back up the temperature after doing batch after patch after batch of fries or chicken or whatever... Those fryer heaters could very easily be on a continuous 3 hours during a lunch or dinner rush
  9. #9
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by JFletcher View Post
    Well I dont know how busy my restaurant is going to be. It hasnt been constructed yet. Which is safer electrical point to assume continous or non continous load?
  10. #10
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,986
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    You need to look at the definition of a continuous load in article 100.