    180612-1702 EDT

    Redwood Infrared:

    Get a good scope, amplifier, and well shielded (magnetically and electrostatically) microphone, plot the sound waveform, and measure its fundamental frequency and harmonics. Expect a relation to 60 Hz line. When synced to AC line does the sound waveform drift in time? Are there other frequencies unrelated and not synchronized with the power line.

    Also look at line current.

    Sound level increasing with load current (generated current) means the sound originates from magnetic field forces. Is the sound level about the same anywhere along the conduit?

    Is the frequency much higher than 60*3*2 = 360 Hz?

    .

  2. #42
    Join Date
    Aug 2008
    Location
    San Francisco
    Posts
    685
    Quote Originally Posted by Redwood Infrared View Post
    ATSman, forgive me but I keep coming back to this and I'm having trouble parsing your second situation. I'm not sure what you mean by mismatch when you say the 120v hot conductors were connected to the ground conductors - that sounds like a straight up short circuit to me? Can you please clarify?
    Yeah, my age is showing What I meant to say was the NEUTRAL and GROUND conductors (120v hot, neutral, ground 3-wire) were crossed at the plug/socket connection causing the neutral current to return on the ground paths back to the supply subpanel. These net currents generated the EMI like a transmitter antenna that cased the screen jitter. Not sure if this is possible with the newer type LCD/ LED monitors. Can anyone comment on that issue?
    Am I in shape?? I get plenty of exercise pushing my luck!!

  3. #43
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    6,843
    180612-2141 EDT

    To make acoustic measurements you may need a non-magnetic, non-conductive, acoustic transducer (microphone) coupled thru a plastic tube to a remote electrical microphone to avoid errors from high magnetic and electric fields near the noisy cable.

    Note: a hairpin loop of wire with the same magnitude and waveform of current flowing in both conductors, but in opposite directions has a high opposing force between the two wires. Without mechanical restraint this will tend to open toward a circular shape.

    With an AC current this force will vary from zero to a maximum twice per cycle. Thus, the potential for vibration is at double the AC frequency. Three wires with three phase power and the vibration fundamental should be 6 times the fundamental.

    .

  4. #44
    Join Date
    Jul 2013
    Location
    Renton, WA
    Posts
    824
    Quote Originally Posted by gar View Post
    180612-2141 EDT



    With an AC current this force will vary from zero to a maximum twice per cycle. Thus, the potential for vibration is at double the AC frequency.

    .
    Not to confuse OP.

    Never found anything you have ever said to disagree with, but perhaps should rethink that sentence.
    Apply 100Hz ac to loudspeaker, you hear 100 Hz, not 200 Hz:
    Or put another way - apply a dc bias and you hear the same, not shifted. etc. Note: full wave Rectified yes = 2X ac frequency as that is the 'new' ac frequency content.

    Tripletts all in phase, which is why 180 Hz and 540 Hz mentioned earlier, as triplets do not cancel in a 3phase bundle, and high mag forces can result. (note: a common cause of common mode inductors due to core heating due to saturation or delta in delta-wye if high harmonics)

  5. #45
    Join Date
    Jun 2018
    Location
    Arcata, CA, USA
    Posts
    47
    Quote Originally Posted by ATSman View Post
    Yeah, my age is showing What I meant to say was the NEUTRAL and GROUND conductors (120v hot, neutral, ground 3-wire) were crossed at the plug/socket connection causing the neutral current to return on the ground paths back to the supply subpanel. These net currents generated the EMI like a transmitter antenna that cased the screen jitter. Not sure if this is possible with the newer type LCD/ LED monitors. Can anyone comment on that issue?
    Oh well that makes a lot more sense, thanks!

    Wouldn't that cause a similar result to if you just bonded the neutral to the ground in a subpanel?

    For what it's worth, I deployed a cheap Gauss meter phone app yesterday and definitely picked up fields bouncing back and forth between the conduits. I don't know how much stock to put in the numerical values, peaking around 8 Gauss, but qualitatively they were 6 to 8x between conduits compared to what I measured anywhere else around their circumference and about 10 to 20x background levels. Nowhere did it affect the LCD on my phone, and nowhere in the building have occupants reported problems with computers or screens, only the annoying audible impacts.

  6. #46
    Join Date
    Jun 2018
    Location
    Arcata, CA, USA
    Posts
    47
    Quote Originally Posted by junkhound View Post
    Not to confuse OP.

    Never found anything you have ever said to disagree with, but perhaps should rethink that sentence.
    Apply 100Hz ac to loudspeaker, you hear 100 Hz, not 200 Hz:
    Or put another way - apply a dc bias and you hear the same, not shifted. etc. Note: full wave Rectified yes = 2X ac frequency as that is the 'new' ac frequency content.

    Tripletts all in phase, which is why 180 Hz and 540 Hz mentioned earlier, as triplets do not cancel in a 3phase bundle, and high mag forces can result. (note: a common cause of common mode inductors due to core heating due to saturation or delta in delta-wye if high harmonics)
    I did try what I think is a slightly better audio spectrum analyzer phone app yesterday - this one seemed to filter out background noise a bit better but might need some slight calibration. I got pretty well defined peaks at about 124 and 248 Hz, which I would imagine if I had good calibration would actually be exactly 120 and 240. These were very comparable values to what I was able to measure near the utility pad transformer outside the building.

  7. #47
    Join Date
    Jun 2018
    Location
    Arcata, CA, USA
    Posts
    47

    Reporting out results from 3rd site visit

    I spent another few hours at the site yesterday investigating the mysterious conduit hum. This time we had the installing electrician there - and he does in fact appear very highly motivated to get the bottom of it and wants it fixed as much as anybody. We also consulted over the phone with the utility rep who oversaw the power quality monitoring effort at the inverter combiner main, ACSD, and buildng MSP several months ago.

    I am still compiling my notes for reporting out to the client but briefly just to address the main questions that have been put to me by this crowd:


    • The parallel 4” EMT has a total of 3 EMT 90° bends plus one pull box for a total of 4 corners.
    • The EMT runs at slightly varying distances apart from one bend to the next, from a couple inches to about a foot apart.
    • Conduit is clamped tightly to (hung from) horizontal uni-strut that is bolted directly to horizontal building frame members along about 80% of its length. For some reason on the remaining 20% the used much less rigid 2-hole hangers bolted directly to the building frame. This less rigid section is at the end toward the “load side” or farthest from the inverters. I’m not certain yet whether this corresponds to where it gets the loudest or not – still haven’t had good full sun weather so my own personal observations of the phenomena have been limited.
    • Because the building frame member spans are 6 feet in most places, the average span between conduit clamps is 12 feet.
    • Downloaded Advanced Spectrum Analyzer Pro to my phone and found the hum appears to have resonant peaks very near 120 and 240 Hz. They are probably exactly those values but I imagine this tool is not very finely calibrated.
    • Not sure how to approach the math but is it likely there's a relationship between the resonant frequency and the distance between clamps?
    • It appears to be resonating most loudly along the longest run that goes right through the middle of the building, which is also where they are farthest apart. Need to spend a bit more time doing a methodical audio survey along its length when conditions are better.
    • EMF readings from a phone app Gauss meter were positive. I did not have time to plot out the values linearly along the conduit but will return to do so if it’s sunny this afternoon.
    • Can’t recall if I mentioned it before, but if you physically grab the conductors in the ACSD, there is a very obvious vibration that can be felt in all three phases, with a notably greater magnitude in the B phase. The vibration is there even when current is low enough there’s not much of an audible hum. Without vib analysis it’s not feasible to quantify. Hmmm…phones have accelerometers in them now, is there an app for that? YEP. Will install and try that out next vist too.
    • We measured current along all 3 phases simultaneously with a single CT and found there is definitely a non-zero current there, ranging from 1.5 to 3 amps as solar output varied between about 60 and 90 kW (about 75% capacity), or up to 240A per phase. At the same time we saw up to 10A total on the parallel grounds, so – if I understand correctly – when you factor in RMS that sort of balances out even if it’s an undesirable way to get those electrons home. This positive result would seem to be pretty significant although it’s still unclear what’s causing it. We don’t have monitoring equipment available to trend this over a few days but I’m trying to track something down to accomplish that.
    • The utility rep did not think this result was unusual, that 1 to 1.5% current unbalance is common in large solar arrays. Still seems significant to me though.
    • We have not, nor as far as I know has the utility, evaluated much on the utility line side. I’m still very interested in the integrity of the ground and neutral bonds in the pad transformer. I did look in the MSP with FLIR and saw nothing unusual…perhaps other than the fact that the main ground pin is not where we thought it would be, and in fact we couldn’t positively find it. There is a small section of exposed copper we think might be it but somebody enclosed it in drywall. Turns out the one I thought was it was just connecting the outdoor backup genset to the building frame, interrupted along its path by a connection to the sprinkler system – which itself had the electrician scratching his head because he came up through trades learning to never do that since the sprinkler system is likely floating and you don’t necessarily want to ground it like you would a cold water inlet or gas pipe. It also turned out that particular conductor, while firmly bonded to the sprinkler pipe, was very poorly bonded to the building frame. Really don’t see how that affects the solar system but we’ll remediate and see if it makes any difference.
    • The electrician will return as soon as possible to address the compromised components we identified with FLIR, starting with hypress lugs etc at the inverter combiner box main switch.
    • OK, maybe this wasn’t so brief but there are a ton of variables here and I’m trying to get my arms around all of them and eliminate them one by one until we’re down to something we can point to as the source of our issue.
    Last edited by Redwood Infrared; 06-13-18 at 11:59 AM. Reason: clarity

  8. #48
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    6,843
    180613-1130 EDT

    junkhound:

    A speaker is a DC magnetic filed with an interacting AC magnetic field. Thus, the fundamental force frequency is the fundamental of the AC field.

    Two AC magnetic fields that are synchronous to each other double the fundamental frequency of the force between them compared to the fundamental of an individual field. +/- or -/+ fields attract, while +/+ or -/- push apart.

    .

  9. #49
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    6,843
    180613-1154 EDT

    In a balanced three phase system when one conductor is at its peak current, the other two conductors have a combined current that is equal in magnitude and opposite in phase. Thus, balance and net zero measured current with a clamp-on around all three conductors. But there are internal forces between the conductors.

    .

  10. #50
    Join Date
    Apr 2006
    Location
    Simi Valley, CA
    Posts
    8,332
    You sure that roof mounted AC units aren't causing the pipe to vibrate, since it sounds like it's hung from the underside of the roof. You say it's worse in the afternoons when the AC's would be running more.


    I'm kind of a look at everything guy.
    I can build anything you want if you draw a picture of it on the back of a big enough check.

    There's no substitute for hard work....but that doesn't mean I'm going to give up trying to find one.

    John Childress