    I have commericial kitchen with following:
    1. Dedicated receptacle outlet for Food processor, full load amps of 13.5 amps, single phase, 120V.
    2. Dedicated receptacle outlet for Commericial food blender, full load amps of 13 amps, single phase, 120V.
    3. Printer shelf with two receptacle outlet, total with both receptacle has full load amps of 16 amps, single phase, 120V.
    Following questions:
    1. What size should the branch circuit breaker be per code?
    2. What would be the nema rating of the receptacle be? Nema 5-15p or 5-20p?
    3. Should nema rating match branch circuit breaker size? So if receptacles are nema 5-15p then breaker be sized 15 amps per code?
    Sent from my SM-G935U using Tapatalk
  2. #2
    Join Date
    Apr 2017
    Boston, MA, USA
    Posts
    85
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    For a commercial kitchen I wouldn't ever use 15 amp receptacles, regardless of the load. You can use 15 amp receptacles on 20 amp circuits as long as there is more than 1 receptacle (a duplex receptacle counts as 2 receptacles).
  3. #3
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Leespark57 View Post
    your saying commericial kitchen 15a receptacles never be used. Should all three items post #1 be in 20 amps receptacle? Lets say its duplex receptacle item #1&2 commericial blender, food processor post#1. Should nema 5-15p not be used?
  4. #4
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If you have a simplex, or single, receptacle, it can be 15 amps for your first two items. See 210.21 B. Both would have a Nema 5-15 receptacle, you cannot put a 20 amp receptacle on a 15 amp circuit.
    As for the third, you would need a 20 amp duplex receptacle on a 20 amp circuit as you cannot put 16 amps of load on a 15 amp receptacle, or breaker. I am not 100% sure on this last item since 15 amp receptacles are rated for 20 amp pass through...
    As for the breaker, you can put 13.5 amps on a 15 amp breaker so long as it's not a continuous load.
    20 amp commercial grade receptacles are more often used in my opinion do to their better construction rather than needing to accept a 5-20 plug... Very little kitchen equipment that I have seen is corded with a 5 - 20
  5. #5
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    24,775
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    After checking the plugs themselves for compatibility, I would use:
    1. 20a single receptacle on a 20a circuit.
    2. 20a single receptacle on a 20a circuit.
    3. 20a duplex receptacle on a 20a circuit.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  6. #6
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    210.21 (b)(2) says where connected to branch circuit supplying 2 or more receptacles, a receptacle shall not supply cord and plug connected load in excess of maximum specified in table 210.21 (b)(2).
    210.21 (b)(3) says where connected to branch circuit supplying two or more receptacles, a receptacle rating shall conform to table 210.21 (b)(3).
    Als see 210.3 for circuit rating meaning.
    So here my interpretation but I could be wrong: duplex receptacle ( 2 receptacles) , one of the two receptacles powers one cord connected blender has full load of 13 amps. So max load is over 12 amps already. Per 210.21 (b)(2) and table 210.21 (b)(2) circuit rating has to be 20 amps. So my overcurrent protection has to be 20 amps
    Now per nec 210.21 (b)(3) and table 210.21 (b)(3) circuit rating of 20 amps receptacle ratings can be 15 or 20 amps.
    So then for the blender 13 amps full load coming from duplex receptacle I must have 20 branch circuit breaker but receptacle rating can be 20 or 15 amps????
    I could be wrong on above??
  7. #7
    Join Date
    Dec 2010
    Tennessee NEC:2017
    Posts
    5,112
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    I would put all 20A receptacles as they are better built, IMO.
    If you aim at nothing, you will hit it every time!
  8. #8
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by codequestion View Post
    So here my interpretation but I could be wrong: duplex receptacle supplied by one cord connected blender has full load of 13 amps. So max load is over 12 amps already. Per 210.21 (b)(2) and table 210.21 (b)(2) circuit rating has to be 20 amps. So my overcurrent protection has to be 20 amps
    A duplex receptacle counts as two receptacles. If you have a Simplex receptacle, a receptacle with the ability to accept one plug on the yoke instead of two, and that is the only receptacle on the circuit, you can load it to 15 amps for a 5 - 15, or 20 amps for a 5 - 20.
  9. #9
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    6,042
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Also note that job specs or 110.3 (B) may require you to use 20 amp receptacles and breakers even if NEC minimum would allow a 15.
  10. #10
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by JFletcher View Post
    1. Food processor is Robot Coupe CL50 Gourmet.
    2. Blender is Vitamix 62826.