    Below is the code reference for NEC 110.26. I would appreciate some feedback on this and how it applies to the pictures below. This pipe is a plumbing vent pipe which was installed thru the electrical room. Is this indeed 'dedicated space'? Feedback?
    Click image for larger version.
  2. #2
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,998
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    It is not in the dedicated space required for that panel.
    Rob
    All responses based on the 2014 NEC unless otherwise noted
  3. #3
    Join Date
    Dec 2007
    Posts
    35
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    How about dedicated space of the transformer?
    Last edited by charlie b; 06-11-18 at 06:07 PM. Reason: Removed unnecessary copy of photo
  4. #4
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    20,149
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Please do not confuse dedicated space (directly above or below the panel vertically) with working space (in front of panel, including above and below panel front height.)
    Both are required (although not necessarily in every situation) but the rules are different.
    Sent from my XT1585 using Tapatalk
  5. #5
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,998
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by ngd4130 View Post
    Not required.
    (E) Dedicated Equipment Space. All switchboards, switch-
    gear, panelboards, and motor control centers
    shall be located
    in dedicated spaces and protected from damage.
    Rob
  6. #6
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    19,438
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    I agree: not a problem.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  7. #7
    Join Date
    Jun 2018
    Philadelphia
    Posts
    1
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes, I also agree, this code starts by saying (The Workspace, which this panel is, the vent pipe is not)
  8. #8
    Join Date
    Dec 2007
    Posts
    35
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thank you to those who replied! The idea that we have this site to ask questions and bounce them off so many professionals is OUTSTANDING! This makes the electrical standards and the electrical industry even stronger and safer!