    I have service switchboard that has main breaker. The switchboard's main breaker load side feeder breaker has feeder cables feeding trough with bus in same room. The bus then has two taps. Both to two disconnect which feeds two different tenant space out of the room
    I know feeder cables from swbd fdr bkr to trough are feeders. Would taps in trough be called the feeder taps? If not then what its called?
    Sent from my SM-G935U using Tapatalk
  2. #2
    Join Date
    Jul 2003
    New Jersey
    Posts
    27,002
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    If these are on the line side of the service disconnect(s) they are service entrance conductors not taps.
    Rob
  3. #3
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    They are in load side of the service.
  4. #4
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,394
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by codequestion View Post
    Unless the cables feeding the bus in the trough are big enough to be protected by the main breaker, I would call this a code violation.
    Bob
  5. #5
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by petersonra View Post
    No no they are. Feeder cables and the bus are big enough to be protected by the switchboard feeder breaker.
  6. #6
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    5,358
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Yes, they would be feeder taps
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  7. #7
    Join Date
    Jul 2017
    MD, USA
    Posts
    628
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    But the feeder cables terminate at the bus still call the two taps for tenant space disconnects feeder taps?
  8. #8
    Join Date
    Jul 2003
    New Jersey
    Posts
    27,002
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Then there is no tap, what you have is a splice.
    Rob
  9. #9
    Join Date
    Jun 2004
    Posts
    5,358
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    Details are sketchy, but sounded like there were taps coming off the feeder bus. Not sure what the bussed thing is, if it's one of those "bussed gutters" or a busway, but either way sounds like it's being used as a feeder.
  10. #10
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    40,197
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The bus itself is a feeder, presuming it has current carrying capacity no less then the overcurrent device protecting it.