I don't see ser as meeting the requirements

680.25 Feeders. These provisions shall apply to any feeder
on the supply side of panelboards supplying branch circuits
for pool equipment covered in Part II of this article and on
the load side of the service equipment or the source of a
separately derived system.
(A) Wiring Methods.
(1) Feeders. Feeders shall be installed in rigid metal conduit
or intermediate metal conduit. The following wiring methods
shall be permitted if not subject to physical damage:
(1) Liquidtight flexible nonmetallic conduit
(2) Rigid polyvinyl chloride conduit
(3) Reinforced thermosetting resin conduit
(4) Electrical metallic tubing where installed on or within a
building (5) Electrical nonmetallic tubing where installed within a
building
(6) Type MC cable where installed within a building and if
not subject to corrosive environment
(2) Aluminum Conduit. Aluminum conduit shall not be
permitted in the pool area where subject to corrosion.


(B) Grounding. An equipment grounding conductor shall be
installed with the feeder conductors between the grounding
terminal of the pool equipment panelboard and the grounding
terminal of the applicable service equipment or source of a
separately derived system. For other than feeders to separate
buildings that do not utilize an insulated equipment grounding
conductor in accordance with 680.25(B)(2), this equipment
grounding conductor shall be insulated.


(1) Size. This conductor shall be sized in accordance with
250.122 but not smaller than 12 AWG. On separately derived
systems, this conductor shall be sized in accordance
with 250.30(A)(3) but not smaller than 8 AWG.


(2) Separate Buildings. A feeder to a separate building or
structure shall be permitted to supply swimming pool
equipment branch circuits, or feeders supplying swimming
pool equipment branch circuits, if the grounding arrangements
in the separate building meet the requirements in
250.32(B).
 

bphgravity

Senior Member
Location
Florida
Please refer to Section 680.25 of the 2014 NEC:

680.25 Feeders. These provisions shall apply to any feeder on the supply side of panelboards supplying branch circuits for pool equipment covered in Part II of this article and on the load side of the service equipment or the source of a separately derived system.

(A) Wiring Methods.

(1) Feeders. Feeders shall be installed in rigid metal conduit or intermediate metal conduit. The following wiring methods shall be permitted if not subject to physical damage:

(1) Liquidtight flexible nonmetallic conduit
(2) Rigid polyvinyl chloride conduit
(3) Reinforced thermosetting resin conduit
(4) Electrical metallic tubing where installed on or within a building
(5) Electrical nonmetallic tubing where installed within a building
(6) Type MC cable where installed within a building and if not subject to corrosive environment

Exception: A feeder within a one-family dwelling unit or two-family dwelling unit betvveen remote panelboard and service equipment shall be permitted to run in flexible metal conduit or an approved cable assembly that includes an insulated equipment grounding conductor within its outer sheath. The equipment grounding conductor shall comply with 2S0.24(A)(5).
 