Thread: Underground feeder junction box

  1. #1
    Join Date
    Mar 2011
    Posts
    11

    Underground feeder junction box

    I am installing a 350' long run of PVC, 240V single phase feeder underground.
    Am I permitted to put a quazite pull box somewhere in that run? There will be no splices in the pull box.

  2. #2
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,767
    Yes, there is nothing in the code that either requires or prohibits that box.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,036
    You can even bury it if you can comply with the exception in 314.29.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4
    Join Date
    Mar 2011
    Posts
    11
    Quote Originally Posted by don_resqcapt19 View Post
    Yes, there is nothing in the code that either requires or prohibits that box.
    That's what I thought, just wanted to make sure I wasn't missing something.
    Thank you