User Tag List
Results 1 to 4 of 4
Thread: Underground feeder junction box
  1. #1
    Join Date
    Mar 2011
    Posts
    13
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I am installing a 350' long run of PVC, 240V single phase feeder underground.
    Am I permitted to put a quazite pull box somewhere in that run? There will be no splices in the pull box.
  2. #2
    Join Date
    Feb 2003
    Illinois
    Posts
    24,133
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes, there is nothing in the code that either requires or prohibits that box.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)
  3. #3
    Join Date
    Jul 2003
    New Jersey
    Posts
    27,232
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    You can even bury it if you can comply with the exception in 314.29.
    Rob
  4. #4
    Join Date
    Mar 2011
    Posts
    13
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by don_resqcapt19 View Post
    That's what I thought, just wanted to make sure I wasn't missing something.
    Thank you