    Circuit Size

    Doe sthi make sense to have a 3P-20A breaker with 4 #6's and a disconnect switch fused at 15amps? That's wrong I think.
    Attached Images Attached Images  

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,036
    What's the purpose of the disconnect switch? On the surface it doesn't make much sense but we could be missing some details.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    May 2013
    Location
    Massachusetts
    Posts
    2,397
    The #6 is above and beyond what the NEC requires for ampacity reasons, unless there is a serious factor like high ambient temperature, or extreme conductor bundling, or both.

    #12 is what the NEC requires for a 20A circuit. The 15A fused disconnect downstream doesn't override this, until you get downstream of it.

    That being said, if you run #6 for voltage drop or any reason unrelated to ampacity, you have to proportionally upsize the EGC. In this case, it means it would be the same size as the rest of the conductors.

  4. #4
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    26,036
    Quote Originally Posted by Carultch View Post
    That being said, if you run #6 for voltage drop or any reason unrelated to ampacity, you have to proportionally upsize the EGC. In this case, it means it would be the same size as the rest of the conductors.
    Good point the #10 EGC with the #6's is possibly a violation.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  5. #5
    Join Date
    Oct 2015
    Location
    US
    Posts
    675
    Quote Originally Posted by Carultch View Post
    The #6 is above and beyond what the NEC requires for ampacity reasons, unless there is a serious factor like high ambient temperature, or extreme conductor bundling, or both.

    #12 is what the NEC requires for a 20A circuit. The 15A fused disconnect downstream doesn't override this, until you get downstream of it.

    That being said, if you run #6 for voltage drop or any reason unrelated to ampacity, you have to proportionally upsize the EGC. In this case, it means it would be the same size as the rest of the conductors.
    Y would you say a #6 is needed if you upsize for voltage drop do you not use 250.122 table to size the egc

    Sent from my SM-G950U using Tapatalk

  6. #6
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,252
    Quote Originally Posted by nickelec View Post
    Y would you say a #6 is needed if you upsize for voltage drop do you not use 250.122 table to size the egc

    Sent from my SM-G950U using Tapatalk
    Table 250.122 is the general rule. 250.122(B) would apply if upsizing for voltage drop, and it would require 6 AWG EGC in OP's situation if conductors are sized like they are because of voltage drop.

    Put a 60 amp breaker on it and then 10 AWG EGC is fine though.

    Makes sense yet it doesn't, right?
    I live for today, I'm just a day behind.

  7. #7
    Join Date
    Jul 2006
    Location
    SE USA as far as you can go
    Posts
    2,678
    I don't believe the OP provides enough information to derive an accurate response to the question.
    What is the load served?
    Why #6?
    What is the distances involved?

    Otherwise it's all speculation.
    "Just because you're paranoid, doesn't mean they're not out to get you"