    Quote Originally Posted by don_resqcapt19 View Post
    I think the grounding electrode system and GECs are required. The only real difference between the rules for a grounded and ungrounded transformer is that the ungrounded one does not have a system bonding jumper.
    Where would the requirement for a GEC be in the NEC for an ungrounded Delta and where would you connect it?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  2. #22
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,233
    Quote Originally Posted by infinity View Post
    Where would the requirement for a GEC be in the NEC for an ungrounded Delta and where would you connect it?
    Metal parts likely to become energized, I imagine. As mentioned, the case of the step up transformer would be connected to the primary EGC, while the case of the step down transformer would be bonded to the GEC of the resulting separately derived system. If the run is connecting two buildings, IMHO there is no requirement to bond the two GESs together. If in the same building there must be a wire bond between all ground electrodes, probably in the form of an EGC connecting the two ends, even though there is no grounded conductor.

  3. #23
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,306
    Quote Originally Posted by infinity View Post
    Where would the requirement for a GEC be in the NEC for an ungrounded Delta and where would you connect it?
    IT is analogous to a detached structure under current code with separate N-G. The GEC lands on the ground bar, but doesnt hit a conductor of the system. See 250.30(B)
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  4. #24
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,164
    Sounds like a waste of time. There are 8-500 kcmil EGC's run to the primary and since the secondary is #2 a #8 GEC landed with those 8-500's would be a joke.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  5. #25
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    23,577
    Quote Originally Posted by infinity View Post
    Where would the requirement for a GEC be in the NEC for an ungrounded Delta and where would you connect it?
    250.30(B)
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)