User Tag List
Page 3 of 4 FirstFirst 1 2 3 4 LastLast
Results 21 to 30 of 35
Thread: 4160 Delta Secondary Grounded or Ungrounded
  1. #21
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,862
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by don_resqcapt19 View Post
    I think the grounding electrode system and GECs are required. The only real difference between the rules for a grounded and ungrounded transformer is that the ungrounded one does not have a system bonding jumper.
    Where would the requirement for a GEC be in the NEC for an ungrounded Delta and where would you connect it?
    Rob
  2. #22
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    20,030
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    Metal parts likely to become energized, I imagine. As mentioned, the case of the step up transformer would be connected to the primary EGC, while the case of the step down transformer would be bonded to the GEC of the resulting separately derived system. If the run is connecting two buildings, IMHO there is no requirement to bond the two GESs together. If in the same building there must be a wire bond between all ground electrodes, probably in the form of an EGC connecting the two ends, even though there is no grounded conductor.
  3. #23
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    5,210
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    IT is analogous to a detached structure under current code with separate N-G. The GEC lands on the ground bar, but doesnt hit a conductor of the system. See 250.30(B)
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  4. #24
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,862
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Sounds like a waste of time. There are 8-500 kcmil EGC's run to the primary and since the secondary is #2 a #8 GEC landed with those 8-500's would be a joke.
    Rob
  5. #25
    Join Date
    Feb 2003
    Illinois
    Posts
    23,961
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    250.30(B)
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)
  6. #26
    Join Date
    May 2018
    Ohio
    Posts
    339
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    i would be more concerned with your primaries. what are you doing with the neutral? i need to refresh my memory but systems with wye primaries can have some serious issues.
    http://apps.geindustrial.com/publibrary/checkout/GET-3388B?TNR=White%20Papers|GET-3388B|
    are you really wiring them wye-delta?
    or are you just saying wye because you have 120/208? but actually wiring it delta
  7. #27
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    we investigated a fatal involving ungroundd delta
    common in some mining
    bonding of all frames was not in place
    a phase faulted to one piece of equipment
    a different phase faulted to a different piece of equip in close proximity to the first
    the victim came in contact with both while moving thru the tightly packed equip room
  8. #28
    Join Date
    Jun 2004
    Posts
    5,210
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Wire-Smith View Post
    If i may nit pick a bit....Im not exactly sure what you mean by "wiring it delta". Obviously, generally the winding configuration is fixed and not changeable. Even if it was, changing from wye to delta or vice versa would change the voltage change ratio. I suspect you mean "delta" in the "jargon" sense of three phase conductors with no neutral. A wye delta transformer would be fed with three phases and no neutral. The point on the primary would float. Bad things can happen if the primary neutral is landed or the wye point bonded. Wye wye transformers have some potential issues, as the paper notes.
  9. #29
    Join Date
    May 2018
    Ohio
    Posts
    339
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    you've never seen a three phase transformer that you can configure the primary anyway you want? i know there not as common as they used to be.
    and either way i'm still asking him whether it truly is a wye-delta transformer or if he is just calling it that because he is using 120/208 system.
    i believe a floating wye primary can come with many problems as well, i need to refresh my memory though.
    http://forums.mikeholt.com/showthread.php?t=53682
    https://www.eng-tips.com/viewthread.cfm?qid=374777
  10. #30
    Join Date
    May 2018
    Ohio
    Posts
    339
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    maybe it's not as big a deal as i think since he might be using 3p breakers on primary feeder, what i have heard about using wye primary on is MV distribution that typically use fuses.
Posting Permissions
  • You may not post replies
  • You may not edit your posts