Thread: 4160 Delta Secondary Grounded or Ungrounded

  1. #1
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,170

    4160 Delta Secondary Grounded or Ungrounded

    We have several 3Ø, 208-4160 WYE/Delta step-up transformers. How are these typically grounded, corner ground or are they typically installed as an ungrounded Delta?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,170
    Bump, have I finally stumped the engineers on this forum?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    Apr 2016
    Location
    Georgia
    Posts
    454
    Quote Originally Posted by infinity View Post
    Bump, have I finally stumped the engineers on this forum?
    I’ve never seen this before nor have I researched it - but why couldn’t you do either or? Personally I think you’d be better off with a corner grounded delta; at least you’d have reference point - plus we rarely see ungrounded deltas these days.


    Sent from my iPhone using Tapatalk

  4. #4
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,234
    IMHO a lot depends on whether the voltage will be stepped back down again after a long run (motivation was VD) or whether the 4160 will be utilization voltage for equipment (and if so, what kind.)

    If just a distribution run to step-down transformer, the risk of high voltage to ground caused by restriking arc fault may not be catastrophic. But no disadvantage to corner grounding either.
    If run to utilization equipment, unless it is an industrial process where unplanned shutdown is problematic, I would avoid ungrounded operation.
    Would the difference in max line to ground voltage be a safety issue for your environment?

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,170
    The service voltage of 208Y/120 is stepped up to 4160 and then run vertically up through the building where it is stepped back down to 208Y/120. Right now the design calls for a ungrounded Delta, I was just wondering if ungrounded is the typical set up for these types of systems.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #6
    Join Date
    Jan 2016
    Location
    PA
    Posts
    5,473
    weird set-up

    why not take the service at 4160 wye?
    how many floors?
    how many 208 taps/xfmrs?
    The difference between genius and stupidity is that genius has its limits.

  7. #7
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,170
    There are 4-4000 amp services in the building all 208Y/120. There are about 10-208 to 4160 step up and another 10-4160 to 208y/120 step down tranformers, all step ups are setup as ungrounded. The step ups are Wye/Delta and the step downs are Delta/Wye.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  8. #8
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,315
    Quote Originally Posted by infinity View Post
    There are 4-4000 amp services in the building all 208Y/120. There are about 10-208 to 4160 step up and another 10-4160 to 208y/120 step down tranformers, all step ups are setup as ungrounded. The step ups are Wye/Delta and the step downs are Delta/Wye.
    Wow
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  9. #9
    Join Date
    Jun 2004
    Location
    Cherry Valley NY, Seattle, WA
    Posts
    4,315
    I think ungrounded would be fine. You already have ungrounded stuff there, keeps it all the same. Also it sounds like there will be people maintaining this stuff that know what they are doing. Finally, regarding the potential over voltage issue from restriking faults, I would think pretty much everything you would install nowadays would be 15KV class so you have plenty of headroom if something along those lines were to happen.
    Ethan Brush - East West Electric. NY, WA. MA

    "You can't generalize"

  10. #10
    Join Date
    Dec 2011
    Location
    Wisconsin
    Posts
    338
    Quote Originally Posted by infinity View Post
    We have several 3Ø, 208-4160 WYE/Delta step-up transformers. How are these typically grounded, corner ground or are they typically installed as an ungrounded Delta?
    250.20(C) permits such systems to be grounded, but does not require them to be grounded.

    (C) Alternating-Current Systems of over 1000 Volts.
    Alternating-current systems supplying mobile or portable
    equipment shall be grounded as specified in 250.188. Where
    supplying other than mobile or portable equipment, such
    systems shall be permitted to be grounded.