Results 1 to 8 of 8
Thread: Per Unit Calculation help
  1. #1
    Join Date
    Apr 2007
    Posts
    198
    It's been a while since I used per-unit calculation so I am embarrassing to say that I am drawing a blank when I ran into this. I requested the utility for available fault current at the transformer I was give this value.
    250MVA transformer (138kv to 38kV), Z=11% with 100MVA. They told me to use infinite bus for my calculation.
    So, I just need to find the new Z for 250MVA transformer right? Is this formula correct to find new Z?
    Z (new) = Z (old) x ( S (base)/S (new) ) = 11 x ( 100/250 ) = 4.4%
    Is this right? It seem Z is too low for this size transformer. I guess I can go back to my old power system book and verify but I thought asking here would be easier and more accurate. Thanks,
  2. #2
    Join Date
    Jan 2016
    PA
    Posts
    5,466
    close
    z old x s new/s old ~ 27.5%
    you can check by doing sc i calc for each s
    The difference between genius and stupidity is that genius has its limits.
  3. #3
    Join Date
    Jan 2016
    PA
    Posts
    5,466
    long way
    you may need the actual ohmic value anyways
    vbase 38kv
    100 mva base
    zbase = 38kv^2/100 mva = 14.44 ohm
    zact = 0.11 x 14.44 = 1.5884 ohm per ph or 2.7512 3 ph
    250 mva base
    zbase = 38kv^2/250 mva = 5.7760 ohm
    z pu = 1.5884/5.7760 = 0.2750 pu or 27.5%
    100 mva sc i = 100 mva/(sqrt3 x 38kv 0.11) = 13821 A
    250 mva sc i = 250 mva/(sqrt3 x 38kv x 0.2750) = 13821 A
    38kv / 2.7512 = 13821
  4. #4
    Join Date
    Apr 2007
    Posts
    198
    Quote Originally Posted by Ingenieur View Post
    long way
    vbase 38kv
    100 mva base
    250 mva base
    Thanks!! I knew I could get the right answer here.
  5. #5
    Join Date
    Jul 2006
    SE USA as far as you can go
    Posts
    2,618
    Quote Originally Posted by elec_eng View Post
    Infinite bus just means that the amount of fault current through the transformer will only be limited by the transformer impedance itself. It appears what the utility gave you is the impedance of the system either on a 100MVA base or they are saying 100MVAsc; can't tell from the post. However, they are telling you to base your design on an infinite bus.
    Thus a 250MVA transformer with impedance of say 8.5% (based on HV KVBIL of 650 and LV KVBIL of 150) will have an MVAsc = 250MVA/0.085 = 2941MVAsc
    @ 38kV that is around 45kAsc.
    However, those numbers may present a problem for 38kV rated equipment. 45KA is out of the range of 38kV gear either vacuum, dead tank or SF6. the limit is 40KA, also the maximum current rating is going to be 3000A but that require fan cooling.
    To limit the current on infinite bus system, the maximum amount of fault current is going to need to be around 38kA (a little margin) thus you need an impedance on the transformer of around 10 to 10.5%. But that doesn't solve the issue of max continuous current which would limit the transformer MVA to around 165MVA or even less depending on manufacturer.
    "Just because you're paranoid, doesn't mean they're not out to get you"
  6. #6
    Join Date
    Jan 2016
    PA
    Posts
    5,466
    imo they gave him a 250 mva xfmr that had its pu z tested/measured at 100 mva
    above 10-15% of rating xfmr v, i and hence s are linear, so z is constant
    as most know the method to measure pu z (in this class each one is tested)
    short the sec and apply v source to prim
    increase v until sec i = rated, in this case due to testing equip limitations/safety they only went to 40% of rating
    100 mva or 1520 A, valid since 40%>>10-15%
    the test v applied to achieve this is 0.11 x 138000 = 15180 v
    prim i = 1520/(138/38) = 418.55A
    z = 15180/418.55 = 36.27 ohm 3 ph or 20.94 1 ph
    on a pu base
    zbase = 138kv^2/100 mva = 190.44 ohm (76.1 on a 250 mva basis)
    pu = 20.94/190.44 = 0.1100 or 11%
    or
    vbase = ibase x zbase and vtest = ibase x zact
    combine/sub/rearrange: vtest = vbase/zbase x zact
    vtest/vbase = zact/zbase = pu z = 15180/138000 = 0.11 or 11%
    if they attemped to test at rated 250 mva
    i prim 1045
    i sec 3798
    vtest 2.5 x 15180 = 37950
    test power 100 mva = 11 mva
    test power 250 mva = 68.7 mva
    quite a difference, alot of it heat
    on a 250 mva base
    vtest/vbase = 37950/138000 = 27.5%
    or z = 37950/1045 = 36.32 ohm 3 ph or 20.97 1 ph (same as abv within rounding)
    pu z = 20.97/76.1 = 27.5%
    more than anyone needs to know about pu z lol
  7. #7
    Join Date
    Jul 2006
    Posts
    2,618
    Typically, the utility is not going to give you the impedance of a transformer on 100MVA base, mostly because, well they don't need too. They would just supply the nameplate data, but the OP is unclear on this point. They typically will give system data on a 100MVA base, but either provide R and X 3ph and 1ph, or X/R ratio. The fact they said use infinite bus for a 138kV-38KV system is odd from my experience since that is a transmission level voltage and typically those guys have system study info that can be provided.
  8. #8
    Join Date
    Jan 2016
    PA
    Posts
    5,466
    Quote Originally Posted by kingpb View Post
    the fact they told him to use infinite bus tells me the 11% is the 250 mva xfmr pu z on a 100 mva basis
    if it was sc mva he could calc system impedance (but not resolve it into r + jx without the x/r ratio
    if they are saying 100 mva sc on the primary that makes no sense since mva sc < 250 mva rating
    if 100/0.11 ~ 910 mva primary
    or less than 13 ka sec
Posting Permissions