    2
    We are wiring a gym addition on a school in South Carolina and they don't use city or county inspectors the go thru a company to do inspection. The inspectors are telling us that when tying up lights we must tie up all four corners of the light and wrap the tie wire around itself 3 times within a inch and it must be tight. Also tie wire must be going in the same angle as the other peices of tie wire or we fail. Didn't know if anyone else has run into this or if we are just getting bullied into doing this.
  2. #2
    Join Date
    Feb 2003
    Bremerton, Washington
    Posts
    7,837
    That is a building code requirement. NEC only requires the luminaire to be fastened to the grid.
    Moderator-Washington State
    Ancora Imparo
  3. #3
    Join Date
    Dec 2011
    Ocala, Florida, USA
    Posts
    2,538
    Quote Originally Posted by Redskins92 View Post
    Agree with Tom if that is for the GRID not the light. That would never be the electrical contractor's responsibility, but I think it is actually the ceiling grid instructions not the building code per se. In some places, including California you are required to install a ceiling wire in opposite corners, so two each to the light itself. Never seen a requirement for 4 corners.
    I know what I don't know, and I know where to go to find it!
  4. #4
    Join Date
    May 2011
    CA
    Posts
    34
    don't forget your earth quake clips securing fixture to grid.
  5. #5
    Join Date
    Dec 2011
    Ocala, Florida, USA
    Posts
    2,538
    Quote Originally Posted by IMFOTP View Post
    They are called hurricane clips in Florida.
  6. #6
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,774
    I think some places go overboard on this. Newer troffers and now LED panels are much lighter then old troffers used to be. Some maybe even lighter then the tile that would otherwise go in the same hole, the tiles don't ordinarily get extra support or securing
    I live for today, I'm just a day behind.
  7. #7
    Join Date
    Jun 2018
    Posts
    2
    Its ridiculous here. Your tie wire cant touch any other trades stuff all four pieces of tie wire must be going in the same angle and must be twisted tightly 3 times with in a inch. We have to paint the tie wire a certain color also. Also have to pull huricane clips which isn't a problem but also had these seismic rated clips on the light also that secure them to the grid.
    Sent from my LGL164VL using Tapatalk
  8. #8
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    4,318
    Quote Originally Posted by kwired View Post
    Good point. Installed some 2x4 led panels today. They weight about half of what a tile weighs....
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  9. #9
    Join Date
    Feb 2003
    Fl
    Posts
    17,138
    Most of NC is in seismic Category C and the requirements for suspended ceilings can be found in this publication and depending on the specs it may or may not be the electricians responsibility but unfortunately it probably is.
    Roger
    Join Date
    Dec 2011
    Ocala, Florida, USA
    Posts
    2,538
    I reread this. If it is anything like doing school work in California, this is likely a spec not a code. Or possibly a desire. No matter where the inspector is required to give you a reference to enforce a rule so ask for it. Independent inspectors are usually hired to enforce both specification and code so they have every right if there is documentation that requires this work. Other than a clearly written spec I doubt they can find a rule. If the spec wasn't in division 16500 (26) fixtures but instead in the acoustical ceiling spec I would argue that it is the ceiling contractor's job to perform this work. As far as 3 turns in 1" THAT is a typical building and manufacturer's requirement for all ceiling wires.