User Tag List
Page 1 of 2 12 LastLast
Results 1 to 10 of 13
Thread: Minimum Service Size
  1. #1
    Join Date
    Jul 2007
    Posts
    409
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I know the NEC says that dwelling units must have a service size no less than 100 Amps.
    I just want to break this down a bit:
    1) If I have my main service going to a house panel first then off this house panel I have a branch breaker feeding an individual dwelling unit. Does this mean that this branch breaker cannot be less than 100A?
    2) Is this 100A min. service size limited to dwelling units only? IE- If I have a warehouse with tiny loads, can I put a 20A service on it?
    Thank You
  2. #2
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,128
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    230.79 is what you are looking for
    230.79 Rating of Service Disconnecting Means. The service
    disconnecting means shall have a rating not less than the calculated
    load to be carried, determined in accordance with
    Part III, IV, or V of Article 220, as applicable. In no case shall
    the rating be lower than specified in 230.79(A), (B), (C), or
    (D).
    (A) One-Circuit Installations. For installations to supply only
    limited loads of a single branch circuit, the service disconnecting
    means shall have a rating of not less than 15 amperes.
    (B) Two-Circuit Installations. For installations consisting of
    not more than two 2-wire branch circuits, the service disconnecting
    means shall have a rating of not less than 30 amperes.
    (C) One-Family Dwellings. For a one-family dwelling, the service
    disconnecting means shall have a rating of not less than
    100 amperes, 3-wire.
    (D) All Others. For all other installations, the service disconnecting
    means shall have a rating of not less than 60 amperes.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  3. #3
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    5,036
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    It's worth noting the code says service disconnect rating, not service size or rating, which is a bit odd....
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  4. #4
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,128
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by electrofelon View Post
    Yes, but then there is this
    230.42(B) Specific Installations. In addition to the requirements of
    230.42(A), the minimum ampacity for ungrounded conductors
    for specific installations shall not be less than the rating of the
    service disconnecting means specified in 230.79(A) through
    (D).
  5. #5
    Join Date
    Jun 2004
    Posts
    5,036
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Dennis Alwon View Post
    Is that new dennis? I recall this debate but don't remember that section
  6. #6
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,128
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    It's been there forever but everyone seems to ignore it. I have mentioned it many times that is why I don't bring up the fact that 230.79 only refers to the disconnect. It is true but 230.42 clarifies. I don't know why they don't just say the feeder or service conductors need to be sized to 230.79 because, IMO, that is what it means. I know others will argue it.
  7. #7
    Join Date
    Jul 2006
    SE USA as far as you can go
    Posts
    2,728
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Instead of going with minimums, why not go "Bigger is Better".
    "Just because you're paranoid, doesn't mean they're not out to get you"
  8. #8
    Join Date
    Jun 2016
    Tampa, FL, USA
    Posts
    2,007
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kingpb View Post
    Because clients like to spend the minimum amount they can to get what they want.
  9. #9
    Join Date
    Jun 2004
    Posts
    5,036
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Because we like to debate theoretical code situations
  10. #10
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,128
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    Sometimes it just a matter of stating what the code states.