User Tag List
Results 1 to 3 of 3
Thread: suspended cable for light
  1. #1
    Join Date
    Aug 2005
    Lawrenceburg, Kentucky
    Posts
    218
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Good day guys and gals.
    I need to run conductors to a 120v light. The conductors will be suspended overhead from a couple of telephone poles about 100ft. What type of cable or conductors would you guys use for this? I was thinking SOOW but I was thinking there has to be something better for this type of application. There is a guy/messenger wire already installed for support.
    Thanks for the replies.
  2. #2
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    40,176
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I myself would use the same kind of triplexed cable assembly the POCO's typically use for service drops - you can get that in as small as 6 AWG aluminum. Conductor insulation will last seemingly forever compared to SOOW.
    I live for today, I'm just a day behind.
  3. #3
    Join Date
    Aug 2013
    New York, NY
    Posts
    538
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    SOOW would be a bad idea. The jacket will deteriorate pretty quickly with sunlight exposure. 400.12 (4) "Not permitted: where attached to building surfaces" could be cited, but the argument that a pole is a "building" is debatable.
    TC-ER tray cable would work.
    https://www.wireandcableyourway.com/...ray-cable.html
    Uses Permitted:
    336.10 (2) In outdoor locations supported by a messenger wire.
    You'll need a lot of cable ties, and (if your inspector is a stickler) they'll need to be listed:
    https://www.advancedcableties.com/news-event/4208/
    At least make sure the cable ties you use are black, and good quality. The natural white cable ties do not last in the sun. Do the next guy a favor and cut your cable ties off flush; I have a scar on my arm from a sharp cable tie tail.
    336.10 (7) e States that you need to secure the cable at intervals not exceeding 6ft, but I'd go closer. 6ft will look sloppy, IMO. Also, if a cable tie fails in the wind, you don't want your cable "zippering" down off the messenger wire.
    SceneryDriver