    I have a 7200 - 480/277V standard pad mount transformer. The primary is fed from overhead utility line. We de-energized the utility line due to some crane lifts going on in the area.
    We hooked up a 480V generator and tied to secondary of transformer. By doing so, would you see 7200V on primary? I thought a buck boost transformer was needed for this type of application.
  2. #2
    Join Date
    Dec 2016
    Waco, tx
    Posts
    91
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The transformer will most likely have that voltage on the primary which means it will heat up the lines that are feeding even though they are disconnected from utilities. Why not just hook the generator into the panel or disco and isolate the transformer?
  3. #3
    Join Date
    May 2018
    El Dorado, KS, USA
    Posts
    7
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Yes, the primary fuses have been disconnected, so there is no way of back-feeding.
    Running the generator cables through a high traffic building and getting to panel was going to be a hassle. So we decided to hit the transformer.
    Thanks for the feedback.