Thread: EGC tap conductors

  1. #1
    Join Date
    Jul 2017
    Location
    MD, USA
    Posts
    628

    EGC tap conductors

    I have utility service coming into main breaker sized 2500 amps 120/208v three phase. Load side of the main breaker feeds bus. The bus is tapped with 4#600 kcmil to discoonect less than 10 feet. What size equipment ground wire be installed from tap to discoonect 1#350kcmil or 1#3 awg?

    Sent from my SM-G935U using Tapatalk

  2. #2
    Join Date
    Feb 2003
    Location
    Connecticut
    Posts
    2,977
    Quote Originally Posted by codequestion View Post
    I have utility service coming into main breaker sized 2500 amps 120/208v three phase. Load side of the main breaker feeds bus. The bus is tapped with 4#600 kcmil to discoonect less than 10 feet. What size equipment ground wire be installed from tap to discoonect 1#350kcmil or 1#3 awg?

    Sent from my SM-G935U using Tapatalk
    350kcmil

  3. #3
    Join Date
    Jul 2017
    Location
    MD, USA
    Posts
    628
    Quote Originally Posted by david luchini View Post
    350kcmil
    Where in code says that?

    Sent from my SM-G935U using Tapatalk

  4. #4
    Join Date
    Feb 2003
    Location
    Connecticut
    Posts
    2,977
    Quote Originally Posted by codequestion View Post
    Where in code says that?

    Sent from my SM-G935U using Tapatalk
    250.122(G)

  5. #5
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    16,843
    Quote Originally Posted by david luchini View Post
    250.122(G)
    pretty clear

    Name:  Capture.JPG
Views: 63
Size:  63.7 KB

    or you could use metal conduit and not need a wire type EGC at all.
    Bob