    Branch circuit overcurrent protection size

    I have 120v single phase branch ciruit to duplex receptalce that draws 13 amps. Whar would the branch circuit overcurrent.protection size be?

    Sent from my SM-G935U using Tapatalk

  2. #2
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,139
    Since this sounds like a homework question tell us what you think and we will go from there.

    BTW, you need to work on your technical writing before you take the PE exam, "whar" won't get it.

    Roger
    Moderator

  3. #3
    Join Date
    Jul 2017
    Location
    MD, USA
    Posts
    628
    Quote Originally Posted by roger View Post
    Since this sounds like a homework question tell us what you think and we will go from there.

    BTW, you need to work on your technical writing before you take the PE exam, "whar" won't get it.

    Roger
    15 amps next higher rating?

    Sent from my SM-G935U using Tapatalk

  4. #4
    Join Date
    Feb 2003
    Location
    Fl
    Posts
    17,139
    See 210.21(B)

    Roger
    Moderator