    Load center as disconnecting means

    I have a situation in an older residence where a 100 amp feeder is run to an exterior trough and feeds three Sq D single breaker AC disconnects with taps. The trough and disconnects are rusted out and need replaced.
    Is there any problem with just replacing the trough with a 6 circuit NEMA 3 panel and using three breakers as disconnects? The units do not require fuses.
    Thanks in advance

    Steve

  2. #2
    Join Date
    May 2011
    Posts
    4,556
    You haven't mentioned anything that strikes me as a problem.

  3. #3
    Join Date
    Jun 2016
    Location
    Tampa, FL, USA
    Posts
    1,703
    Sounds like what I would do. If the breakers are not in sight of the AC units, you will need to be able to lockout the breakers or set disconnects.
    Last edited by Coppersmith; 06-15-18 at 08:13 AM.

  4. #4
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    37,913
    Quote Originally Posted by Coppersmith View Post
    Sounds like what I would do. If the breakers are not in sight of the AC units, you will need to be able to lockout the breakers or set disconnects.
    Pretty certain there is no option in NEC to have locking means on remote disconnect for an AC unit.