Page 2 of 2 FirstFirst 12
Results 11 to 20 of 20
Thread: 480V, 3PH, UPS with 4 hours backup battery
  1. #11
    Join Date
    Apr 2018
    Grantsville, MD, USA
    Posts
    13
    Quote Originally Posted by Besoeker View Post
    And weighing close to 7 tonnes. And costing maybe about $25k
    One of our customers is a wind farm that has a grid-tied battery backup, 16 sea cans full of batteries on top of a mountain, 8,000kWh of storage. http://www.energystorageexchange.org/projects/164
    And yes, there are certainly cheaper options out there than batteries!
  2. #12
    Join Date
    Jan 2018
    Centerville
    Posts
    7
    Based on my past projects, I could see this being a $300k custom system not including installation, shipping, engineering, drawing package etc.
    Total seems like $400k to $450k for a quick swag number.
  3. #13
    Join Date
    Sep 2008
    UK
    Posts
    12,024
    Quote Originally Posted by publicgood View Post
    $25k would be cheap. Thinking way more.
    I was basing it on what we paid for Yuasa VRLA units.
    Si hoc legere scis nimium eruditionis habes.
  4. #14
    Join Date
    Jul 2006
    Posts
    8,117
    I wonder how Tesla Power Wall batteries would stack up to this application? I’ve not yet been involved in pricing them, but the concept is the same. I have a customer right now who has a solar farm backed up by them, he wants to run a 250HP drive and pump motor from it, I’m only involved in the drive part of it. It might be rude to ask him what the Tesla batteries cost him, but he also may not actually know because it was a packaged installed system with the solar panels, trackers, inverters and grid tie system. Rude of not, I’m going to ask him when I get a chance.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  5. #15
    Join Date
    Jun 2017
    WI, USA
    Posts
    383
    Understood.
    Note: Due to the volume of electrolyte, by code, each battery cabinet would require thermal runaway management. That cost alone is about $10k, per cabinet.
  6. #16
    Join Date
    Sep 2008
    UK
    Posts
    12,024
    Understood.
    Our systems were on open frame battery racks in an air conditioned switch room. Yes, that is also a cost factor.
  7. #17
    Join Date
    Apr 2007
    Berkeley, CA
    Posts
    1,743
    Quote Originally Posted by Jraef View Post
    Powerwall is $5,900 for 5 kW AC power and 13.5 kWh AC capacity. Currently in short supply.
    Tesla Powerpack might fit the bill. Specs are 50 kW AC power and 210 kWh AC capacity per unit. I'm unclear on cost, per wikipedia it was $400/kWh 1.5 years ago.
    Cheers, Wayne
  8. #18
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    each motor draws ~23 A
    you spec 2 items: inverter and batteries
    you need ~100 A x 4 hr ~ 400 A hr, use 500
    you need 1.35 x 480 or 650 vdc
    using a 24 v cell ~ 28 in series at 100 ahr each
    so 5 sets in parallel, 140 each 24 v 100 ahr batteries
    80 kw/100 kva inverter
    this is a common industrial ups
    inrush should be minimal during transition
    you can start the motors is sequence
    https://eaton-upssystems.com/?gclid=...SAAEgJlvfD_BwE
  9. #19
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    some pricing http://www.inverterpower.co.ke/index...va-unit-prices
    80 kw $60k 1/2 hr
    you need more batteries figure $70k plus install
    a 24 v 100 ahr battery $70 x 140 x 3.5/4 = $8600
    you get 0.5 hr with the ups
  10. #20
    Join Date
    Jan 2014
    chicago, il, USA
    Posts
    404
    Why not recommend to the customer a combination of both a genset and a UPS. The UPS would only be there for the transition from utility to generator power so it would not have to be sized for more than a couple of minutes of runtime but you would probably want to specify something in the 15-minute range. You could certainly use a UPS with less than a minute of capacity but I would think you would want it sized to handle a complete system shutdown in the event that the generator failed for some reason.
    With this design the UPS handles the transition while the genset spools up and then once the genset is online the ATS would transition from the UPS to the genset. Make sure you include in your calculations whatever controls equipment is required to operate these motors. This could involve one or more computer systems, a control cabinet, Etc.
    The world is round, you will get there no matter what path you take.