    Quote Originally Posted by Dale001289 View Post
    Maybe I should write a PI. Article 501.125(B) is very poorly written and continues to be a source of confusion - as witnessed by this thread. I could make it infinitely better by simply adding a few key words. But then again, I've always excelled in logical thinking and creative writing.
    That is a good idea. BTW it's Section 501.125(B). The Article is 501.

    You might also try for a Formal Interpretation. It is a lot tougher to get, but it can be quicker if successful.
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.

  2. #42
    Join Date
    Apr 2016
    Location
    Georgia
    Posts
    490
    Quote Originally Posted by rbalex View Post
    That is a good idea. BTW it's Section 501.125(B). The Article is 501.

    You might also try for a Formal Interpretation. It is a lot tougher to get, but it can be quicker if successful.
    Good advice. I will look into further. Thanks.


    Sent from my iPhone using Tapatalk

  3. #43
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    37,098
    Quote Originally Posted by don_resqcapt19 View Post
    How does an undamaged fan create a spark?

    Division 2 does not require that the equipment not be able ignite a flammable atmosphere under ALL possible conditions, just that it not do so under normal operating conditions.


    Besides unless it is an old motor cooling fans will be non ferrous anyway.
    I live for today, I'm just a day behind.