    Generator Grounding and NEC 230.6

    I am designing a project where the client has an existing stand alone building (metal shed) for a stand-by generator that basically backs up the entire campus loop if the utility power goes out. The generator is rated at 480Y/277 and the voltage is stepped up outside of the building to 12470Y/7200V to feed acampus loop. We aren't doing any work on the Medium Voltage side only the Low Voltage Side (480Y/277V) in the metal shed building.

    In the building the client is upgrading from (1) 1400KW diesel generator with an ATS to having (3) 500KW diesel generators paralleled with a paralleling switchboard. The neutral and ground will be bonded in the paralleling switchboard and the generator breakers are all in the paralleling switchboard, no breakers at the generators.

    If this is the case, would I have to comply with NEC 230.6 and concrete encase the portion of the feeders from the generators to the paralleling switchboard since they will be installed over head (above grade) and system won't be grounded until it reaches the paralleling switchboard?

  2. #2
    Join Date
    Aug 2010
    Posts
    188
    I want to make sure I am not in violation of NEC 230.3...that's why I am thinking I need to comply with NEC 230.6.

  3. #3
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    37,921
    Quote Originally Posted by Shujinko View Post
    I want to make sure I am not in violation of NEC 230.3...that's why I am thinking I need to comply with NEC 230.6.
    Sounds like there is no service conductors involved in what you are doing to me, if so then nothing in 230 should apply.
    I live for today, I'm just a day behind.

  4. #4
    Join Date
    Aug 2010
    Posts
    188
    Quote Originally Posted by kwired View Post
    Sounds like there is no service conductors involved in what you are doing to me, if so then nothing in 230 should apply.
    Service Conductors are defined in the NEC as "The conductors from the service point to the service disconnecting means." In my case I am talking about the conductors from the generators to the paralleling switchboard. The "service disconnecting means" are in the paralleling switchboard. Therefore, I think a picky electrical inspector/plans reviewer might pick up on this as being in violation of NEC 230.3 and NEC 230.6. Thoughts?

  5. #5
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    4,568
    The definition of "Service" relates it to the utility. The generator power is delivered by feeders.
    Ron

  6. #6
    Join Date
    Aug 2010
    Posts
    188
    Quote Originally Posted by ron View Post
    The definition of "Service" relates it to the utility. The generator power is delivered by feeders.
    Yes, I think I was getting confused with the definition of a feeder and a service conductor as it relates to a generator. In the NEC a feeder is defined as "All circuit conductors between the service equipment, the source of a separately derived system, or other power supply source and the final branch circuit over current device." As a generator is considered a separately derived system I think the situation I have describes a set of feeders not service conductors. NEC Exhibit 100.7 shows the definition of a feeder as it relates to a generator very well.

    On a different note I have to make sure that I am in compliance with all the grounding requirements for a separately derived system in NEC 250.30(A) since my source of a separately derived system and the first OCP/Disconnecting means are at different locations.
    Attached Images Attached Images  

  7. #7
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    4,568
    Quote Originally Posted by Shujinko View Post
    On a different note I have to make sure that I am in compliance with all the grounding requirements for a separately derived system in NEC 250.30(A) since my source of a separately derived system and the first OCP/Disconnecting means are at different locations.
    Hopefully the step up transformers you are feeding are Delta - Wye where the delta winding is the 480V side.

    That way you can have the N-G bond at the paralleling SWGR and not bring Neutrals to the transformer (only 3W +G) and not have to deal with circulating current issues.
    Ron

  8. #8
    Join Date
    Aug 2010
    Posts
    188
    Quote Originally Posted by ron View Post
    Hopefully the step up transformers you are feeding are Delta - Wye where the delta winding is the 480V side.

    That way you can have the N-G bond at the paralleling SWGR and not bring Neutrals to the transformer (only 3W +G) and not have to deal with circulating current issues.
    We are connecting to an existing step-up XFMR, Y - Y, 480Y/277V primary and 12470Y/7200 secondary. What's your experience with problems with the circulating currents on a step up transformer?

  9. #9
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    4,568
    Quote Originally Posted by Shujinko View Post
    We are connecting to an existing step-up XFMR, Y - Y, 480Y/277V primary and 12470Y/7200 secondary. What's your experience with problems with the circulating currents on a step up transformer?
    Try to confirm how the existing is connected. Is the existing N-G bonded at the gen and at the step up secondary or not? Is there a Neutral on both the primary and secondary of the transformer brought to / from?
    Ron

  10. #10
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    19,534
    Quote Originally Posted by Shujinko View Post
    We are connecting to an existing step-up XFMR, Y - Y, 480Y/277V primary and 12470Y/7200 secondary. What's your experience with problems with the circulating currents on a step up transformer?
    There are general problems with a transformer with a wye primary and delta secondary, which you often end up with when reversing a standard delta in, wye out transformer.
    If you connect the neutral on the wye primary side, any imbalance in primary phase voltages can cause circulating currents in both the delta secondary and the wye primary.
    There have been quite a few threads explaining this in detail, so I will not go into it in depth here.

    Sent from my XT1585 using Tapatalk