User Tag List
Results 1 to 9 of 9
Thread: Generator grounding
  1. #1
    Join Date
    Jun 2018
    Richmond, VA
    Posts
    2
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Generator grounding
    How should a commercial non portable generator be grounded that has
    case a - ats that switches neutral
    case b - ats that doesnt switch neutral
    do you have to put ground rod at generator in either case ?
  2. #2
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    2,025
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    There are many ways to skin this cat -- install instructions generally have detail schematics showing options to your examples
    CircuitRyder --- Unfortunately not all good ideas are code enforceable.
  3. #3
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    2,025
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    250.30 might help
  4. #4
    Join Date
    Nov 2010
    Fort Collins, Colorado
    Posts
    2,864
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by mrkc949 View Post
    Case A: Must be installed as a SDS. Bonded neutral at genset main breaker. Must have a GES connected at that point. Must have EGC on load side of genset main breaker.
    Case B: Install as a non-SDS. Must NOT bond the neutral at genset. Must have EGC to genset. No GES required. You could optionally connect a GES to the the frame of the genset.
  5. #5
    Join Date
    Feb 2012
    Washington State
    Posts
    148
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by texie View Post
    That is pretty succinct.
    This should be a sticky...
    Kirchoff and Ohm...the only laws that make sense
  6. #6
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    40,183
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Usually you are matching the ATS to the system (SDS or non SDS) more so then matching the system to the ATS.
    I live for today, I'm just a day behind.
  7. #7
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,383
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I seem to recall you are required to use the structure's GES if a connection to a GES is required.
    Bob
  8. #8
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    40,183
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by petersonra View Post
    You do need to tie into the structure's GES. Nothing prohibits installing an additional "supplemental electrode" though.
  9. #9
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,383
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    the OP asked if he HAD to put in ground rods. The answer to that is they would appear to be optional.
    but he does have to tie into the structure GES regardless of whether he adds ground rods or not. this is not optional IMO.
    Bob
Posting Permissions