Thread: Flourescent Lighting Fixture Starters

  1. #31
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    6,898
    180704-2401 EDT

    hbiss:

    The article may suggest that inductive kick starts the lamp arc when the starter contact opens, and there may be such a kick. But I would not agree that this is of any importance.

    What is important is that the filaments are hot and thus electron emitters, and that there is sufficient supply voltage to cause arc conduction in the fluorescent tube. This has to and does reoccur every 1/2 cycle. You can see a high initial voltage drop across the tube that drops substantially as current increases thru the half cycle. When voltage drops below holding voltage then the arc stops. On the next half cycle the cathode shifts to the other end of the tube, and a new arc has to be started. After this initial heating, and on a continuing basis this all occurs with no opening and closing of the starter.

    The purpose of the starter is to initially heat the filaments so that they are good emitters of electrons. Current thru the heaters to support the arc keeps the heaters hot from cycle to cycle after the filaments have been initially heated, and the heater thermal time constant is long enough that too much cooling does not occur from cycle to cycle.

    .

  2. #32
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    6,898
    180705-0720 EDT

    In my previous post heater and filament mean exacly the same thing.

    In the early radio days a tube had at least a filament and a plate (a diode) (Edison effect). With DC used to power the filament there was no hum introduced. When AC was used to power the heating element, then it became necessary to separate the heating function from the emitting function, and the indirectly heated cathode was developed.

    An additional comment on starting the arc. Change the inductor in the ballast to a resistor. You still need the AC peak voltage to at least exceed the breakdown voltage of the bulb to start the arc discharge. And this has to occur every half cycle. The very first cycle and every one thereafter.

    .

  3. #33
    Join Date
    Aug 2016
    Location
    North Augusta, SC USA
    Posts
    25
    Quote Originally Posted by LarryFine View Post
    A starter is closed at first, so each filament sees 60v. After the lamp fires,the starter is open, so it has 120v across it. The ballast is a simple 1-coil inductor. See the diagram in post #2.
    The fixture has two starters, so does that make a difference in the voltage the starter sees. Since the supply voltage is 120V, I would think that during the replacement of the starter the mechanic experienced 120V shock. If otherwise, please let me know. Thanks.

  4. #34
    Join Date
    Aug 2016
    Location
    North Augusta, SC USA
    Posts
    25
    Quote Originally Posted by hbiss View Post
    You say yourself you measured 5 volts so you have to believe that. It's limited by the ballast of which there are many different designs. So you can't say that, under the same conditions they all will cause the same voltage to be present on the starter to ground.

    But don't go by what I say. Take the fixture, remove the starter and measure the voltage to ground from each of the two starter contacts in the socket. Remember too that the starter can be inserted either of two ways (there is no polarity) and you say that the starter had one side shorted to the case. So you have to think about whether the starter was removed and re-inserted before you took your voltage readings.

    So you can answer your own question by assuming that the shorted side of the starter was connected to the highest of whatever you measure at the socket.

    Now whether it caused the shock that was reported is another matter.

    -Hal
    Please understand, the 5V was measured from the starter's casing to ground with a Tegam 110. The mechanic used different grounds, such as the fixture, conduit, and receptacle ground. All readings taken stabilized at 5 volts. When the starter was removed and checked with a Fluke from the prong to the casing, it measured a short. So I'm still finding it hard to believe a 5V measurement.

  5. #35
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    23,011
    Quote Originally Posted by Nardie View Post
    The fixture has two starters, so does that make a difference in the voltage the starter sees. Since the supply voltage is 120V, I would think that during the replacement of the starter the mechanic experienced 120V shock. If otherwise, please let me know. Thanks.
    If the fixture has two starters, it also has two tubes. Each starter-and-tube acts as an independent fixture, just sharing the line and neutral electrical supply, so everything we've said here still applies.

    In my opinion, with an internal short between one starter pin and the starter case, the voltage to ground is most likely to be 60v during start, or 120v but through one tube-end filament, so somewhat lower.

    However, the steady 5v described in the above post suggests that the pin that was shorted to the starter case was the pin connected to the filament that was in turn connected to the neutral, and the voltage came through the gas in the tube.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  6. #36
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    3,656
    There are inconsistencies in your story or at least the story that was related to you that cause some doubts. One is that both lamps failed to operate until the one "offending" starter was replaced. As Larry states, with those fixtures with two lamps, each lamp is independent of the other with its own ballast and starter. So the that starter couldn't affect the other lamps operation.

    Second, you never went back and tested the starter socket to see what voltage was present on both of the pins. Assuming that the starter was shorted one pin to case, that would have told you the two voltages possible.

    Third, did you ever disassemble the starter to see where the short was? In those days when they made starters with aluminum cans, there was a cardboard sleeve inside to insulate the can from the live parts.

    Fourth, the mechanic reported an electrical shock that entered his right side and exited his left side while his left hand was free and while standing on a fiberglass ladder. At most, with 120v to ground on the starter can he could have felt something in his right hand. That's it. His story is suspect because of the absence of the possibility of conduction from arm to arm and it's an old story often told by those cautioning about electric shock. "Electric shock from hand to hand travels across the chest can cause your heart to stop, so be careful and keep one hand in your pocket when working on live wiring."

    Not that anybody is allowed to work live these days.

    -Hal

  7. #37
    Join Date
    Aug 2016
    Location
    North Augusta, SC USA
    Posts
    25
    So, the other day I disassembled the starter and this iswhat I found. The filament was completely black, which tells me a shortoccurred. One of the leads to the capacitor (I think this a capacitor, not surenot familiar with starters) and pin terminal was missing. The casing had asmall indention on the internal side. The starter is a Damar 40W starter. Whenthe starter was removed, we noticed obvious damage since the external pins andphenolic base was awkward. When the continuity check was performed between theexternal pins to the casing, one pin was shorted to the casing. I believe thispin was the one with the missing lead and caused the indention. This is basedon the external pin configuration during removal. During the inspection, itappears the casing of the Damar starter is weaker compared to some otherstarters I pressed against. So, I’m thinking that possibility duringre-installing the starter, the casing collapsed due to the pressure applied bythe mechanic. Please remember he noticed the starter didn’t seem alignedproperly and that is why the mechanic removed it. Once removed, he didn’tnotice any damage. Yet once removed after the event, we noticed damageimmediately. So, I am confident this damage happened during re-installation. I’mwondering has anyone else experienced this type of event with a Damar starter?Also, I believe based on the internal damage that is why we measured 5 volts fromthe casing to ground. Any suggestions?

  8. #38
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    6,898
    180714-2427 EDT

    Nardie:

    Look at the circuit diagram for a starter type fluorescent light.

    The fluorescent tube has a filament at each end of the tube. When excited from a current thru the filament to produce a low red glow the voltage across the filament is about 4 V on one bulb I tested.

    Before an arc (plasma) is established in the tube the current path in the starter type fixture is neutral to one end of a first filament. Next current goes thru the filament to its other terminal. This terminal goes to one terminal of the starter. Initially the starter has a normally closed contact between its two terminals, thus it is a short. The second terminal of the starter goes to one end of the second filament. The other end of the second filament goes to one end of the ballast inductor. The other end of the ballast inductor goes to 120 hot or some higher voltage.

    The ballast inductor is designed to provide a desired current thru the fluorescent tube after the plasma is established.

    In turn the filaments are designed to heat to a desired temperature when the current thru the two filaments is that which results from the series combination of two filaments and the current limiting inductor. It appears this happens when the voltage across one filament is about 4 to 5 volts.

    The starter has a voltage sensor that initially closes a shunting contact when voltage is applied and there is no plasma conduction..

    Note that the starter is a short across where the plasma will develop, and the plasma cannot develop until that short is removed. Internal to the starter is a time delay mechanism (thermal) to delay opening the shunting contact to allow time for the filaments to heat.

    When the contact opens, and the filaments are adequately heated, then when the voltage across the the tube reaches voltage breakdown the plasma is established. The starter is designed so that tube voltage is not great enough to reclose the shunting contact.

    Once the tube is in plasma mode, then the current thru the plasma is sufficient to keep the filaments heated. What voltage is observed across a filament under self heating I don't know.

    The voltages within the started are dependent upon where in the sequence you are. While preheating within a few volts of neutral (common or ground). Before preheat, no starter, one terminal is near neutral, the other near hot or something higher. After plasma is present no greater than fluorescent tube voltage drop.

    .

  9. #39
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    23,011
    Quote Originally Posted by gar View Post
    In turn the filaments are designed to heat to a desired temperature when the current thru the two filaments is that which results from the series combination of two filaments and the current limiting inductor. It appears this happens when the voltage across one filament is about 4 to 5 volts.
    Wouldn't the filaments each see close to 60v? I don't believe the inductor drops that much voltage, which you're saying is 110v.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  10. #40
    Join Date
    Apr 2008
    Location
    Ann Arbor, Michigan
    Posts
    6,898
    180715-1015 EDT

    Larry Fine:

    You need to do some experiments.

    A fluorescent tube is a gaseous discharge device. As such it is an approximate constant voltage load with a negative resistance characteristic. This type of load must be driven by an approximate constant current source. A voltage source with a high internal impedance compared to the load impedance can be viewed as an approximate current source.

    Experiments you should do. In a starter type fixture with the fluorescent tube installed replace the starter with a short. Measure the voltage drop across one filament, and measure true RMS current thru the filaments. Do this just long enough to get your readings. This current should be higher than when the tube is driven without the short. If held too long might burnout the ballast (like an hour or faction of).

    Next remove the short and install the starter. Apply power to the fixture. After the tube illuminates measure the voltage across one filament. Measure the true RMS current thru the tube.

    If you put even 8 to 10 V on a filament it would burnout quite quickly.

    .