    Flourescent Lighting Fixture Starters

    Just recently I had an E&I mechanic experience an electrical shock while reinstalling a fluorescent lighting fixture starter. The starter is a FS-4 30-40W. The mechanic was replacing the bulbs for the fixture, and noticed the starter seemed not to be installed correctly since the fixture did not illuminate once the bulbs were replaced. So the mechanic removed it, inspected the starter, and reinstalled it after noticing no damage. When he twisted the starter into place he felt an electrical shock, and described the sensation as "it lit me up". He was standing on a fiberglass ladder, and stated "that only his right hand touched the starter". When a voltage test was performed with a low voltage proximity tester on the starter and fixture, the tester did light up only in proximity of the starter not the fixture. When the starter was tested with a Tegam 110 voltage tester, the voltage measured was 5V to ground. There was several different grounds used to include the light fixture. The starter was removed and damage was noticed. During a continuity test between the starter's male terminals to its casing, one male terminal was shorted to the starter's casing. The starter was replaced, and the light fixture began operating. So my question is this since I'm not very familiar with fluorescent lighting starters, what is the voltage conducted through the starter? Is it the normal line voltage of 120V, or does it operate at a lower voltage? I am trying to understand why when tested, the voltage on the starter's casing was measured only at 5V, yet the mechanic stated he felt the shock enter his right side and exited his left while standing on a fiberglass ladder, i.e. note he also stated his left hand was touching nothing, not grounded. Is it due to the current of through the starter, or something else? Any help would be greatly appreciated. Also, the mechanic is fine and was released by medical personnel with no restrictions. Thanks

  2. #2
    Join Date
    Mar 2016
    Location
    The Motor City, Michigan USA
    Posts
    851
    An old-fashioned fluorescent fixture with a magnetic ballast and a mechanical starter connects one side of the starter to the hot wire.
    The ballast and filament will limit current, but limit it to a much higher level (~1 amp) than is hazardous to a person. (~0.02 amps)

    Name:  old_fluorescent_light_wiring_diagram.jpg
Views: 265
Size:  14.4 KB

  3. #3
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    3,973
    ... the mechanic stated he felt the shock enter his right side and exited his left while standing on a fiberglass ladder, i.e. note he also stated his left hand was touching nothing, not grounded.
    Sounds like he was repeating the oft told story of someone who was actually shocked. Fear of electricity can make people believe things that didn't happen. Or maybe he is looking for a comp claim or lawsuit and wanted to cover his a** if something should happen later.

    I could believe that he might have felt something in his hand when he removed and replaced the starter probably since some part of his hand or fingers also contacted the grounded fixture.

    -Hal

  4. #4
    Join Date
    Aug 2016
    Location
    North Augusta, SC USA
    Posts
    25
    I appreciate the replies, however I would still like to know what voltage level the starter operates at? I do think the mechanic felt something, just not what was described. I am unfamiliar with starters in light fixtures, so would the ~1 amp at 5 volts give the mechanic the false sense of an electrical shock, or something else? When we tested the starter for voltage, I'm sure we had a good ground, however we tested with several different grounds, i.e. receptacle, unistrut, light fixture and conduit, and the meter stabilized at 5 volts. I'm a little puzzled so any assistance would be helpful.

  5. #5
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    3,973
    You say yourself you measured 5 volts so you have to believe that. It's limited by the ballast of which there are many different designs. So you can't say that, under the same conditions they all will cause the same voltage to be present on the starter to ground.

    But don't go by what I say. Take the fixture, remove the starter and measure the voltage to ground from each of the two starter contacts in the socket. Remember too that the starter can be inserted either of two ways (there is no polarity) and you say that the starter had one side shorted to the case. So you have to think about whether the starter was removed and re-inserted before you took your voltage readings.

    So you can answer your own question by assuming that the shorted side of the starter was connected to the highest of whatever you measure at the socket.

    Now whether it caused the shock that was reported is another matter.

    -Hal

  6. #6
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    23,703
    Quote Originally Posted by Nardie View Post
    I appreciate the replies, however I would still like to know what voltage level the starter operates at?
    A starter is closed at first, so each filament sees 60v. After the lamp fires,the starter is open, so it has 120v across it. The ballast is a simple 1-coil inductor. See the diagram in post #2.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  7. #7
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,500
    Quote Originally Posted by Nardie View Post
    I appreciate the replies, however I would still like to know what voltage level the starter operates at? I do think the mechanic felt something, just not what was described. I am unfamiliar with starters in light fixtures, so would the ~1 amp at 5 volts give the mechanic the false sense of an electrical shock, or something else? When we tested the starter for voltage, I'm sure we had a good ground, however we tested with several different grounds, i.e. receptacle, unistrut, light fixture and conduit, and the meter stabilized at 5 volts. I'm a little puzzled so any assistance would be helpful.
    What voltage you will measure will depend on whether you are taking measurement during pre ignition of the arc in the lamp, or after ignition, and also depend on working condition of the lamp and the starter.

    With a lamp that hasn't ignited an arc yet and a removed starter - you will have one side of the starter socket at the same potential as the ungrounded conductor and the other side at same potential as the grounded conductor. Plug a properly working starter into the socket and have intact elements at each end of the lamp and you have a series circuit consisting of L1- ballast coil - end element of the lamp - starter - other end element of the lamp - N. There will be voltage drop across each segment of the circuit, but then the lamp is parallel to the starter once it has established an arc - but normally operating starter should be open when the lamp is lit - so it will have same potential across it as the lamp has from one end to the other when lamp is lit one end is directly connected to the grounded conductor - if wired like the drawing in post 2. If someone has input polarity wrong then that end is connected to the incoming grounded conductor - the whole thing still works because it is still 120 VAC across all of it either way.
    I live for today, I'm just a day behind.

  8. #8
    Join Date
    Mar 2016
    Location
    The Motor City, Michigan USA
    Posts
    851
    Before the lamp turns on, the starter is closed and both sides will see "half" of line voltage.
    After the lamp turns on, the starter is open. One side of the starter is "connected" to the grounded wire and sees "zero" voltage; (aka. "white", aka. "neutral") the other side is "connected" to the hot wire and sees "line" voltage.
    (I've used quote marks because there are a few voltage drops here & there and what I said is not literally & precisely true)

    When inserting the starter, there will be a moment when only one pin is in contact with the socket.
    With one terminal of the starter faulted to its casing, its casing might have been energized with line voltage, or half of line voltage, either of which is hazardous.

    The 5 volts you measured is almost certainly the result of voltage drop in the neutral wire. This is entirely normal.
    (there's a little bit of voltage drop in the white wire because current's flowing, and no voltage drop in the green wire because no current's flowing)
    Were you to remove the starter, turn it 180° and re-insert it, you'd probably see almost line voltage on its casing instead of almost zero volts.
    (I am speaking hypothetically. Do not actually try it.)

    It's not unusual to get a small shock while standing on a fiberglass ladder. Fiberglass is an insulator, but it's not a perfect insulator, and a little bit of dirt, moisture or capacitance will allow a little bit of current to flow.

    If this is in a commercial/institutional/industrial building, it's possible that the fluorescent lamps are powered with 277 volts.

    I recommend destroying this starter before disposing of it, to make it impossible for somebody else to repeat this episode.

  9. #9
    Join Date
    May 2005
    Location
    Richmond, Virginia
    Posts
    23,703
    Quote Originally Posted by drcampbell View Post
    I recommend destroying this starter before disposing of it, to make it impossible for somebody else to repeat this episode.
    Or open it and see what caused the connection between internal wiring and the case.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA

  10. #10
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    38,500
    Quote Originally Posted by drcampbell View Post
    Before the lamp turns on, the starter is closed and both sides will see "half" of line voltage.
    After the lamp turns on, the starter is open. One side of the starter is "connected" to the grounded wire and sees "zero" voltage; (aka. "white", aka. "neutral") the other side is "connected" to the hot wire and sees "line" voltage.
    (I've used quote marks because there are a few voltage drops here & there and what I said is not literally & precisely true)

    When inserting the starter, there will be a moment when only one pin is in contact with the socket.
    With one terminal of the starter faulted to its casing, its casing might have been energized with line voltage, or half of line voltage, either of which is hazardous.

    The 5 volts you measured is almost certainly the result of voltage drop in the neutral wire. This is entirely normal.
    (there's a little bit of voltage drop in the white wire because current's flowing, and no voltage drop in the green wire because no current's flowing)
    Were you to remove the starter, turn it 180° and re-insert it, you'd probably see almost line voltage on its casing instead of almost zero volts.
    (I am speaking hypothetically. Do not actually try it.)

    It's not unusual to get a small shock while standing on a fiberglass ladder. Fiberglass is an insulator, but it's not a perfect insulator, and a little bit of dirt, moisture or capacitance will allow a little bit of current to flow.

    If this is in a commercial/institutional/industrial building, it's possible that the fluorescent lamps are powered with 277 volts.

    I recommend destroying this starter before disposing of it, to make it impossible for somebody else to repeat this episode.
    Did they make "preheat" style systems that operate on 277 volts?

    The ballast and one side of the lamp are in series on one side of the "starter" and the other side of the "starter" has just one lamp end in series with a supply conductor. I doubt you would find half the supply voltage at the starter because of different overall impedance on each side of it. But IMO we are both on the right track that the voltage to ground from that starter can vary depending on conditions and can be up to full voltage at times, and with the right conditions, of the supply circuit. I don't know what voltage the lamp is designed to operate at once it has established an arc, but the ballast is going to have whatever difference there is from the input voltage across it. During starting it will be a different voltage because there will be change in overall impedance of the lamp/starter segment of the circuit from what "running" conditions are.
    I live for today, I'm just a day behind.