    250.120 EGC outside cable or conduit

    A 100 amp sub panel in a basement of a house was installed using only three wires. I need to correct this. I believe I am okay running a #8 attached to the outside of the PVC conduit?

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    25,335
    Can't be more than 6'.

    300.3(2) Grounding and Bonding Conductors. Equipment
    grounding conductors shall be permitted to be installed out-
    side a raceway or cable assembly where in accordance with
    the provisions of 250.130(C) for certain existing installa-
    tions or in accordance with 250.134(B), Exception No. 2,
    for dc circuits. Equipment bonding conductors shall be per-
    mitted to be installed on the outside of raceways in accor-
    dance with 250.102(E).

    250.102(E) Installation. Bonding jumpers or conductors and
    equipment bonding jumpers shall be permitted to be in-
    stalled inside or outside of a raceway or an enclosure.
    (2) Outside a Raceway or an Enclosure. If installed on
    the outside, the length of the bonding jumper or conductor
    or equipment bonding jumper shall not exceed 1.8 m (6 ft)
    and shall be routed with the raceway or enclosure.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  3. #3
    Join Date
    May 2018
    Location
    Internet
    Posts
    117
    Quote Originally Posted by infinity View Post
    Can't be more than 6'.
    Equipment grounding Conductor

    250.134(B) "or otherwise run with circuit conductors"

    102 is jumpers. i believe he is referring to EGC, would 102 apply?

    but 300.3 (B)(2) i think forbids it

    "equipment grounding conductors shall be permitted to be installed outside a raceway or cable assembly where in accordance with the provisions of 250.130(C)(non-grounding receptacle replacement) for certain existing installations or in accordance with 250.134(B), exception no. 2, for dc circuits. equipment bonding conductors shall be permitted to be installed on the outside of raceways in accordance with 250.102(E)"
    Last edited by Wire-Smith; 07-02-18 at 11:25 AM.