User Tag List
Page 1 of 3 1 2 3 LastLast
Results 1 to 10 of 22
Thread: Grinder Pump Float Signal wire type and gauge
  1. #1
    Join Date
    May 2007
    Posts
    31
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Have to wire a Meyer grinder located in an outdoor holding tank located 125 feet from panel/alarm inside the residence.
    I'll be feeding the signal wires through 3/4" T&B Smurf conduit. Just wondering the type and gauge wire I need to source for to carry the signals the 125 foot distance from the outdoor grinder to the indoor panel/alarm station. As far as the grinder power, the 2 HP grinder will be fed off a subpanel appropriately fed from the house's main panel. No question(s) regarding that part of the install.
  2. #2
    Join Date
    Jun 2003
    Hawthorne, New York NEC: 2014
    Posts
    4,359
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    All I've ever seen are float switches that can be either LV or 120v. Really no current involved so I see no reason you can't use THWN of a size determined by whatever the OCP is for the control circuit, if any.
    -Hal
  3. #3
    Join Date
    Jan 2016
    Earth
    Posts
    6,049
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    do you have any info on the control panel? mfg/model/pn etc
    most I have seen are 120 but only drive a relay (which drives the contactor)
  4. #4
    Join Date
    Jun 2003
    Posts
    4,359
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Correct. The control panel instructions should have all the information you need.
    -Hal
  5. #5
    Join Date
    Feb 2007
    USA
    Posts
    5,836
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    If the floats are intrinsically safe you might need a shielded wire. Been a while since I have done one.
  6. #6
    Join Date
    May 2007
    Posts
    31
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Grinder pump signal wire gauge
    It is a Simplex panel. Will get the model # tomorrow as it's 300 miles north of my location today. I'm still concerned about "crosstalk" between the single phase 220 and the signal wires (9 of them I believe), in a 1" PVC conduit over a distance of 125'. Grinder is a 2 HP Meyers. I will have 3 floats and the thermal wires and one other signal wire and perhaps a spare. Was thinking if high voltage, then #12 would suffice for signal wires. Power will be tapped off subpanel 35 feet away, so I believe #12 would suffice to power grinder pump.
  7. #7
    Join Date
    Nov 2014
    Miami, Florida, USA
    Posts
    208
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Are you pumping sewage?
  8. #8
    Join Date
    Jul 2006
    Posts
    8,499
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Russs57 View Post
    I can’t imaging another use for a grinder pump...
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  9. #9
    Join Date
    Nov 2014
    Miami, Florida, USA
    Posts
    208
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    If he is, he will need explosion proof seals so methane gas doesn’t travel up conduits. Nobody mentioned so I wasn’t assuming.
    Put the thermal wiring with pump wiring and all the float switches in another raceway.
  10. #10
    Join Date
    Jun 2003
    Posts
    4,359
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Jons View Post
    Why do you think they are "signal" wires? Thermal wires? You mean power for heat tape?
    -Hal
Posting Permissions
  • You may not post replies
  • You may not edit your posts