Thread: VFD Savings

  1. #11
    Join Date
    Jan 2016
    Location
    Earth
    Posts
    6,049
    Quote Originally Posted by don_resqcapt19 View Post
    Ok, I assumed that the reduction of pressure on the discharge valve also resulted in a reduction in flow.
    look at it like this
    you have a valve partially closed, as you open it (reduce press loss) flow increases


    you are correct if you consider an oriface
    as the pump slows down, pressure drops, as does flow

  2. #12
    Join Date
    Apr 2006
    Location
    Springfield, MA, USA
    Posts
    3,231
    Agreeing with ingenieur here.

    The pressure reducing valve has reduced the flow from what it would have been if it were not there. It is like a linear voltage regulator in a series circuit; adjusting its resistance to maintain a constant output pressure.

    The flow through the pipe is the same from one end to the other, again like a series circuit.

    If you remove the pressure reducing valve, you would then somehow reduce the pump output to get the same flow/output pressure at the destination.

    -Jon

  3. #13
    Join Date
    Jan 2016
    Location
    Earth
    Posts
    6,049
    a picture is worth a 1000 words lol

    a pump curve
    heavy black line = pump performance curve
    as head increases flow decreases (as does hp at bottom)

    thin blue line is the system curve, basically friction loss vs flow
    derived from pipe length, friction, fittings, etc
    as flow increases so does friction loss

    the point they intersect is the operating point
    100 ft hd, 1000 gpm, ~30 hp, ~84% eff
    (100 1000 8.34)/(60 550 0.84) = 30.1 hp

    valve influence
    close valve system curve shifts left, open shifts right, always origin = 0

    vfd influence
    shifts the pump curve up/down
    if speed = 1/2 flow drops 1/2

    green line = eff
    Attached Images Attached Images  
    Last edited by Ingenieur; 07-04-18 at 05:37 PM.

  4. #14
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    37,887
    There is going to be some energy lost as heat in the valve/orifice correct? I don't know how significant it will be.

    Energy needed to pump a specific flow rate should remain the same.

    We used to heat a tank of lecithin (gets too thick to pump around room temp) by recirculating water through the heating jacket of the tank. Just the friction of moving the water through the system was enough to work, if we needed a quick boost in heat they would stick the steam hose in the balance tank and give it a shot of heat.
    I live for today, I'm just a day behind.

  5. #15
    Join Date
    Jan 2016
    Location
    Earth
    Posts
    6,049
    tried to show the change from valve to vfd
    removed 50 ft hd from system curve
    lowered (slowed) pump curve to achieve same 1000 gpm
    est new eff ~ 0.65

    hp = (25 x 1000 x 8.34)/(33000 x 0.65) = 10 hp
    pump speed ~ 700/1000 (based on original system curve) 70% or 42 Hz
    Attached Images Attached Images  

  6. #16
    Join Date
    Dec 2006
    Location
    Eastern Oregon
    Posts
    3,594
    Quote Originally Posted by ptonsparky View Post
    Customer with a 100 HP motor pumping from a large tank to two pressure regulating valves. Input pressure to the valves is 96 PSI. Output is 53 PSI on the load side of one of the valves. Assuming for the moment that they are both set the same.

    The only restriction on the inlet side is the short pipe connecting the centrifugal pump to the tank.

    The VFD savings calculator I found indicated payback was in less than 2 months by just changing the speed(s) for x amount of time for each. That would be a quick sell.

    Seems to me that I would also need to know how much water is actually moving at that 53 PSI in the 6"? pipes leaving the PR valves. What other values do I need to make a better SEWAssumptiveG in cost savings for a customer?
    Do you need variable speed to maintain a strict pressure setpoint?

    Or would it be simpler to drop the motor/pump sizes and keep it on a starter if maintaining a precise pressure setpoint isn't that important?

    Nema starters are reliable and considerably cheaper to replace versus a VFD.

  7. #17
    Join Date
    Dec 2016
    Location
    Royal City, WA
    Posts
    199
    Quote Originally Posted by Ingenieur View Post
    a picture is worth a 1000 words lol

    a pump curve
    heavy black line = pump performance curve
    as head increases flow decreases (as does hp at bottom)

    thin blue line is the system curve, basically friction loss vs flow
    derived from pipe length, friction, fittings, etc
    as flow increases so does friction loss

    the point they intersect is the operating point
    100 ft hd, 1000 gpm, ~30 hp, ~84% eff
    (100 1000 8.34)/(60 550 0.84) = 30.1 hp

    valve influence
    close valve system curve shifts left, open shifts right, always origin = 0

    vfd influence
    shifts the pump curve up/down
    if speed = 1/2 flow drops 1/2

    green line = eff
    Ingenieur;

    there is is a difference between a positive displacement pump and a centrifugal Pump. As I’m sure you know.

    a centrifugal Pump designed for 60 hz, will barely develop any pressure or flow at 30 hz. However a positive displacement pump will still deliver full pressure, but only half the flow at half speed. A centrifugal Pump usually need to be run above 45 hz to develop any meaningful flow or pressure

    the Pump affinity laws state
    whrn you double the speed of the impeller;
    you double the flow,
    you square the pressure,
    you cube the horsepower

    https://www.engineeringtoolbox.com/a...aws-d_408.html

  8. #18
    Join Date
    Dec 2016
    Location
    Royal City, WA
    Posts
    199
    Ptonsparky

    since you mentioned that this was in a 3,000 head dairy. I have to assume it is for the effluent system. The potable water system is probably only a few hundred gallons per minute.

    For our non-agricultural members, Many larger CAFO’s (Confined Agricultural Feeding Operations)have a flushing type manure system. Only they have to flush the floor of the entire building.it can take well over a thousand gallons per minute for this system. Much of the water is recirculated. It is not a one pass system.

    it sounds like a much larger than needed Pump was installed, a 40-60 horsepower Pump would be capable of what the existing 100 hp pump is doing, if they never need any more pressure. Yes the best solution would be to replace the 100 hp pump with the correct size Pump. Yes there will be some energy savings with a VFD, but not as much as you might imagine. Why? With the throttling valve you are moving the Pump curve to the left and decreasing the amps the motor is using.

    It seems counterintuitive to most people, but as you close a discharge valve on a centrifugal Pump, the amps go DOWN, not up. The amps can drop almost 50% if you fully close the valve. Now as you throttle a pump the amps go down, but the amps per gallon pump go up as you move away from the BEP (best efficiency point). That is why the most efficient way is to pick a pump that is running at its BEP.

  9. #19
    Join Date
    Jan 2016
    Location
    Earth
    Posts
    6,049
    it all depends on the pump curve and system curve
    the pump may operate at 30 Hz but has lost so much pump eff and motor eff it is not beneficial

    typical curve 30-60 Hz
    Attached Images Attached Images  

  10. #20
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    9,943
    Quote Originally Posted by Dzboyce View Post
    Ptonsparky

    since you mentioned that this was in a 3,000 head dairy. I have to assume it is for the effluent system. The potable water system is probably only a few hundred gallons per minute.

    For our non-agricultural members, Many larger CAFO’s (Confined Agricultural Feeding Operations)have a flushing type manure system. Only they have to flush the floor of the entire building.it can take well over a thousand gallons per minute for this system. Much of the water is recirculated. It is not a one pass system.

    it sounds like a much larger than needed Pump was installed, a 40-60 horsepower Pump would be capable of what the existing 100 hp pump is doing, if they never need any more pressure. Yes the best solution would be to replace the 100 hp pump with the correct size Pump. Yes there will be some energy savings with a VFD, but not as much as you might imagine. Why? With the throttling valve you are moving the Pump curve to the left and decreasing the amps the motor is using.

    It seems counterintuitive to most people, but as you close a discharge valve on a centrifugal Pump, the amps go DOWN, not up. The amps can drop almost 50% if you fully close the valve. Now as you throttle a pump the amps go down, but the amps per gallon pump go up as you move away from the BEP (best efficiency point). That is why the most efficient way is to pick a pump that is running at its BEP.
    It is for their potable water.

    The flush system uses very little additional water.
    Tom
    TBLO