    We have recently reviewed our company's bus torque chart and found some of the values are in line with the bolt mfg suggestions (i.e.- 1/4" - 7/16" bolts) but some of the values were much lower than bolt mfg suggestions (i.e.- 1/2" - 3/4" bolts). I started to update our torque chart to match the bolt manufacturers specifications but I have a concern. The torque chart from Fastenal for a 1/2" Grade 8 bolt is 80ft/lbs. If when running main bus in a 480V switchgear I use 1/2" bolts and torque to 80ft/lbs, what happens when the bus bar heats up during use? Theoretically, the bus bar can go as high as 105deg C; have I gone beyond the suggested torque value of the bolt or did the bolt heat up as well and 'give' with the bus?
    John
  2. #2
    Join Date
    Sep 2004
    Vancouver, WA
    Posts
    735
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Bolting
    This is a complex issue but some manufacturers have written articles on it. The torque depends on the TPI and whether it is lubricated. No simple answer.
    If the bus is copper-copper, then steel or copper bolts with lock washers may be adequate because the coefficients of thermal expansion are similar.
    If one or more bus is aluminum, then 1 or 2 Belleville washer(s) are needed to accommodate the expansion. On a 1/2-13 SS bolt, you take a 6000# Belleville to 40 ft-lb, about 1/2 flat. That puts 3000# of pressure per bolt. As the bus heats, the AL expands, the Belleville gives a little then returns as the bus cools. Without the Belleville, the joint can deform and loosen over time.
    Old school had aluminum bolts with aluminum bus. Now, more often, SS bolt, bronze nut, SS Belleville and flat washers. BZ nut to prevent galling.
    BTW: studies have shown that it is pressure that guarantees a good joint. Joint resistance goes down as pressure goes up.
    e^(i pi) = -1
  3. #3
    Join Date
    May 2015
    Posts
    10
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Thanks Beanland. These connections are for new build Switchgear, so all are copper to copper with grade 8 zinc plated steel bolts. Agreed the tighter the bolt the lower resistance, i just dont want to over-stress the bolt when the bus heats up. I think this is not probable but i definitely want to avoid popping off bolt heads after a few years of heating and cooling.
    John
  4. #4
    Join Date
    Dec 2011
    Ocala, Florida, USA
    Posts
    2,997
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by beanland View Post
    And over torquing can cause the Belleville washer to operate improperly. A Belleville washer, by the way is a cupped washer, so basically a spring.
    I know what I don't know, and I know where to go to find it!
  5. #5
    Join Date
    Jul 2009
    Ware Shoals, South Carolina
    Posts
    1,260
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Check the switchgear manufacturers instructions. Over torque can create hot spots in the joint because the excess pressure can deform the copper, resulting in catastrophic failure.
    Advise is a dangerous gift, even from the wise to the wise.
  6. #6
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,854
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    The Eaton gear we use has a 50 ft# torque rating for 1/2" hardware and 20 ft# rating for 3/8" hardware. The four bolts connecting the 4000 amp bus links together are 3/8" carriage bolts torqued at 20 foot pounds.
    Rob
  7. #7
    Join Date
    Oct 2013
    MD
    Posts
    84
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    You can view NFPA 70B online for free. They have charts from multiple mfrs.
    1/2" Grade 8 Heat-Treated Steel - 75 lbft
    1/2" Coated Silicon Bronze - no lube - 40 lbft
    " " lube - 25 lbft
    1/2" Al - 25 lbft
    1/2" Stainless Steel - 40 lbft
    All based on based on national coarse thread pitch.
  8. #8
    Join Date
    May 2015
    Posts
    10
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Strathead View Post
    Haha...unfortunately, I am the switchgear manufacturer. I am being questioned on our current torquing process and its values versus the bolt manufacturers standard torquing values. The people who created our current charts are long gone (along with the reasoning behind the values). I am hesitant to just use bolt manufacturers values since the bus bar will heat up and expand; I don't think this is considered in the bolt manufacturers values.
  9. #9
    Join Date
    May 2015
    Posts
    10
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by SG-1 View Post
    Infinity, thanks for the information. These values are really close to our original charts. I am just unsure how they were derived.
    John
  10. #10
    Join Date
    May 2015
    Posts
    10
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Smoothops 10, these are the values i am looking to use now. My concern is that if i torque to these values and then the bus bar heats up, i may go over the recommended value.