    I can clearly see MOPD is 40A for this 460V 3 phase compressor.
    Next I see Minimum Circuit Ampacity is 31.9A
    Two or more people told me that this is the load. I disagree.
    The load is Fan Motor FLA(1.0*2) + Compressor Motor RLA (7.3+10.3) =19.6A
    Who is correct????Name:  HVAC Compressor Label.jpg
  2. #2
    Join Date
    Oct 2013
    MD
    Posts
    84
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    I would use MCA divided by 1.25 for load.
    https://www.titus-hvac.com/softwares...ecalculate.pdf
  3. #3
    Join Date
    Oct 2015
    US
    Posts
    824
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    The math is already factored in there use a 40a breaker or fuse with conductors suitable for 31.9 amps
    Sent from my SM-G950U using Tapatalk
  4. #4
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,854
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    The MCA is the largest component (usually the compressor) *125% + the other loads. Curious as to why do you need to know the actual load?
    Rob
  5. #5
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,623
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by infinity View Post
    How about for feeder and service calculations?
    I live for today, I'm just a day behind.
  6. #6
    Join Date
    Jul 2003
    New Jersey
    Posts
    26,854
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by kwired View Post
    Could be that's why I asked.
    Rob
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    39,623
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by dionysius View Post
    19.6 is the maximum load it is rated for. Conditions of operation will determine actual load, but should not exceed that. Not sure just how they came up with MCA of 31.9, unless there is other load not on the nameplate for some reason. It is usually 125% of largest load plus all other loads. Even taking both compressor figures x 1.25 still doesn't get us all that close to 31.9.
  8. #8
    Join Date
    May 2008
    West Chester, PA
    Posts
    606
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    kwired, I agree, that MCA is a puzzlement.
    Alternate current
    Line to ground and ground to line
    Current alternates
  9. #9
    Join Date
    Apr 2016
    WA
    Posts
    306
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by nickelec View Post
    Elaborate on why you believe 31.9A is the running load. It cannot be that since it would heat up the wire.
  10. #10
    Join Date
    Jun 2003
    Hawthorne, New York NEC: 2014
    Posts
    4,229
    Mentioned
    1 Post(s)
    Tagged
    0 Thread(s)
    Running load is 19.6, the nameplate says wire it with conductors suitable for 31.9, not that the running load is 31.9, and use a maximum of a 40A breaker. So if you could find a 35A three pole you could use it.
    Apparently they are designing for the max starting draw and voltage drop.